[Bldg-sim] Interior window creation
    Nick Caton 
    ncaton at smithboucher.com
       
    Thu May 27 15:54:43 PDT 2010
    
    
  
Alan,  
 
To my understanding, you simply cannot put a window on an interior wall.
The best approximation may be as follows:
1.       Keep the internal wall in it's entirety - this will model heat
transfer to the adjoining space correctly... if it's a large internal
window consider adjusting the internal partition's properties to match
the effective thermal mass/U-value.
2.       Create a new external wall, of any construction layers, on top
of the interior wall with the exact (maybe rounded) area of the window
3.       Create a window on that exterior wall with that exact area and
with matching properties to the real glazing with one exception:  Give
it a ridiculously low U-value to effectively eliminate what would be the
modeled thermal transfer interactions with the exterior.
4.       Assign window shades to model the solar shading effects of the
adjacent space (ceiling/walls).
 
Best of luck!
 
~Nick
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jackson,
Alan
Sent: Thursday, May 27, 2010 5:47 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Interior window creation
 
I am attaching the pd2 and inp, just so someone can confirm they get the
same error. I am on a 64-bit machine so I have been getting weird
warnings and error to begin with back when I was using the wizard.
 
Alan Jackson, LEED AP
KlingStubbins
 
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jackson,
Alan
Sent: Thursday, May 27, 2010 6:43 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Interior window creation
 
I am attempting to create an interior window to allow solar gains to
pass through a sunspace to an adjacent space. I am getting to the
following warning when attempting to create a window component on the
interior wall.
 
 
 
As a work around I changed the wall to EXTERIOR-WALL in order to add the
windows then planned on changing back to INTERIOR-WALL but when I open
the project I get a warning saying "A PARENT EXTERIOR-WALL must be
defined before .."
 
I know you can create interior windows and use them in conjunction with
sunspaces as the DOE2 manual specifically calls out this scenario. 
 
What am I doing wrong?
 
 
Alan Jackson, LEED AP
KlingStubbins
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100527/ef39d968/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100527/ef39d968/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4463 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100527/ef39d968/attachment.png>
    
    
More information about the Bldg-sim
mailing list