[Bldg-sim] Appendix G Chiller
    Demba Ndiaye 
    Demba.Ndiaye at setty.com
       
    Thu May 27 07:51:17 PDT 2010
    
    
  
Marty,
You are probably referring to Appendix G of ASHRAE 90.1-2004. It is about water-cooled chillers: it is implicit in the System-Specific Baseline HVAC System Requirements.
This has been corrected in the 2007 version, which now states explicitly "water-cooled".
______________
Demba NDIAYE
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Snarski, Marty
Sent: Thursday, May 27, 2010 10:31 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G Chiller
Hello, All.
After perusing Appendix G and the LEED book, I've been unable to find the answer to this one:
If I've got a project that's using a Air-cooled Chiller, what baseline chiller do I use?  Appendix G says to use 2 equally sized Screw Chillers.  But, it doesn't say if these have to be air-cooled or water cooled.  I'd imagine there's quite a benefit to compare with a water cooled, when you take into account the cooling tower, etc.
Any ideas if this is alright?
Martin Snarski   LEED(r) AP
Mechanical Engineer
NOTICE:
This e-mail transmission is intended only for the use of the individual or entity named above and may contain information that is confidential, privileged, and/or exempt from disclosure under applicable law. If you are not the intended recipient, you are hereby notified that any review, disclosure, copying, distribution, or other use of any of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify the sender by e-mail at the above address and delete it from your computer system; you should not copy the message or disclose its contents to anyone. The content of the message and or attachments may not reflect the view and opinions of the originating company or any party it is representing.