[Bldg-sim] Natural Ventilation Control in Design Builder
    Paul Carey 
    paul at zed-uk.com
       
    Thu May 13 09:36:32 PDT 2010
    
    
  
Holly,
 
If you use the scheduled mode you should be alright in doing roughly what
you want it to do using the scheduled air flow rates.
 
Essentially you need to set up the Nat Vent Set-Point Temperature on the
Activity tab and you'll see along with that you should have an option for
setting the Max In-Out Delta T.  This should allow you to set the model up
with your scheduled rates, but put a realistic setting in there which means
that natural ventilation will not occur if the Delta T is higher than say 5
deg C.  It means it won't bring in air that is too hot or too cold and will
only bring in as much as is possible with the Delta T that exists, etc.
 
Personally, I don't quite get why you don't just let the model calculate it
for you in calculated mode as I'd hope that way it should be more accurate
rather than trying to muddle together two separate calculations.
DesignBuilder can work out the stack/wind combined flow easily enough.
 
 Kind Regards
 
Paul
 
 
 
 
ZED_LOGO_SMALL
Dr Paul Carey
BSc (Hons) PhD FRSA
Director
Low Carbon Energy Assessor
 
Zero Energy Design Ltd
10A Portland Place
2-22 Mottram Road
Stalybridge
SK15 3AD
 
T:  0161 3386200
F:  0161 3031281
M: 0789 4098012
E:   <mailto:paul at zed-uk.com> paul at zed-uk.com
W:   <http://www.zed-uk.com/> www.zed-uk.com
 
 
cid:image002.jpg at 01CA48E6.60E6D920
 
 
 
 
 
 
 
 
cid:image003.jpg at 01CA48E6.60E6D920
Certificate No: GB16647
 
 
cid:image004.jpg at 01CA48E6.60E6D920
Certificate No: GB16646
 
 
Please carefully consider the environment before you print this email.
 
Company Registered in England & Wales.  Registration No. 5815068
Registered Address: 10A Portland Place, 2-22 Mottram Road, Stalybridge, SK15
3AD, UK.
 
Privilege and Confidentiality Notice:
 
This email and any attachments to it are intended only for the party to whom
they are addressed.  They may contain privileged and/or confidential
information.  If you have received this transmission in error, please notify
the sender immediately and delete any digital copies and destroy any paper
copies.  Thank you.
 
 
 
 
 
 
 
 
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of holly
wasilowski
Sent: 12 May 2010 20:39
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Natural Ventilation Control in Design Builder
 
Hi,
I am working with natural ventilation in DesignBuilder.  In another program
(CoolVent) I calculated varying ACH due to wind and stack effect.  I made a
schedule and input it into DesignBuilder. The problem is, I would like
DesignBuilder to both use my schedule of air changes AND close the windows
when it gets too cold outside.  However, it seems that I can either be in
Scheduled or Calculated mode.  Scheduled mode will use my ACH schedule, and
Calculated mode will close the windows when it's too cold.  It seems I can't
make DesignBuilder take both into account.  Am I missing something?  Thanks!
Holly
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100513/60fa468a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3268 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100513/60fa468a/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3204 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100513/60fa468a/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3183 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100513/60fa468a/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2120 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100513/60fa468a/attachment-0003.jpeg>
    
    
More information about the Bldg-sim
mailing list