[Bldg-sim] Simulating Occupancy Sensors

Karen Walkerman kwalkerman at gmail.com
Mon May 10 09:35:14 PDT 2010


Appendix G allows a certain prescribed lighting reduction allowance for
occupancy sensors.  I believe it is 10-15% of lighting power, depending on
the building.  You can put the reduction in the schedule or in the lighting
power.  If I have some spaces with occupancy sensors, and some without, I
usually reduce the lighting power and use the same schedule.

--
Karen

On Mon, May 10, 2010 at 12:22 PM, amit bhansali <amitbhansali7 at gmail.com>wrote:

> Hello all,
>
> I am trying to simulate an energy model (Baseline and Proposed) for a LEED
> project. I understand that exceptional lighting controls could be used for
> energy savings in Proposed model. I was wondering if I could use the
> lighting schedule as 7:30 to 5:30 on weekdays as 100% in the baseline and
> then change the lighting schedule to match the occupancy schedule for
> simulating with occupancy sensors? Is that a acceptable approach. Please
> advise.
>
> --
> Thanks in Advance
>
> Sincerely,
> Amit Bhansali, M.S. , EIT
> Command Commissioning, LLC
> 8410, Sterling St
> Irving, TX  75063
> www.command-cx.com
> www.godparents.in
> Please do not print this e-mail unless necessary
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100510/c0fbba2a/attachment.htm>


More information about the Bldg-sim mailing list