[Bldg-sim] modeling chilled beams in eQuest
Kendra Tupper
ktupper at rmi.org
Thu May 6 09:39:51 PDT 2010
Oh, I know its not the same - I just couldn't come up with anything that
solved both problems! Trading one evil for another I suppose.....
This is an active chilled beam system in an office building, so the outside
air supply is varying based on cooling load and CO2 sensors - the mechanical
engineer is used VSD ECM motor series FPBs to modulate the outside air
delivered to the chilled beams at the zone level. so it would be impossible
to manually schedule the outside air according to load (that's why we're
using an energy model!). Modeling constant volume induction units conditions
far more outside air than in the actual design, so I figured it might be
more important to account for this, vs the chilled beam cooling at the zone
level.
Kendra Tupper, PE, LEED AP
Senior Consultant
Built Environment Team
Rocky Mountain Institute | T 303-567-8641 | F 303-245-7213 |
www.rmi.org
On Thu, May 6, 2010 at 10:23 AM, Vikram Sami <vssami at yahoo.com> wrote:
> Kendra,
>
> I don't think the PIU approach is really the same - for one you are not
> modelling the cooling at the zonal level with chilled water like a chilled
> beam works.
>
> I haven't modeled a chilled beam with a VAV supply before - mostly because
> in the projects I've used chilled beams (labs) you restrict the supply to
> only ventilation air which is a constant set normally to around 6ACH. Have
> you tried using the Induction unit and assigning a schedule to the fresh
> air? I think you can vary the amount of outside air to each zone that way.
>
> Vishnu - if this is a lab building 20% for fan energy is not completely out
> of the question. Couple of things to check:
>
> 1. When you come out of th eQUEST wizard the fan energy tab is normally
> described in terms of static pressure and not kW/cfm. Make sure you set
> those to default to activate the kW/cfm. You might have already done this
> because the kW/cfm option generally doesn't show up unless you do this.
> 2. to check if the fan energy is coming from your DOAS - try zeroing out
> the fan energy on the DOAS and see if that reduces your fan contribution.
> That way at least you'll know if your barking up the right tree.
> 3. If this is a lab, make sure you model your exhaust correctly. While
> Chilled beam systems don't use fan energy on the supply side, the labs will
> use fans on the exhust side. These will need to be captured on the zonal
> exhaust level.
> 4. Unless your supplying air neutral from the DOAS, you will need to
> capture the cooling effects of the supply air (Kendra - this is where it
> gets tricky for a VAV supply).
>
> Hope this helps
> *Vikram Sami*
> **
> ------------------------------
>
>
> --- On *Thu, 5/6/10, Kendra Tupper <ktupper at rmi.org>* wrote:
>
>
> From: Kendra Tupper <ktupper at rmi.org>
> Subject: Re: [Bldg-sim] modeling chilled beams in eQuest
> To: "Ellen Franconi" <efranconi at rmi.org>
> Cc: "vishnu" <vishnu at kalpakrit.com>, "bldg-sim" <
> bldg-sim at lists.onebuilding.org>
> Date: Thursday, May 6, 2010, 8:42 AM
>
>
> The other thing at work here is that the Induction units and the DOAS are
> constant volume, so you're going to pay a fan energy penalty for this - so
> first, make sure you only have one zone per Induction unit in eQUEST. In
> real life, the DOAS can send variables amounts of air (based on load) to
> chilled beams, but this can't be modeled with the Dummy zone/DOAS approach.
> If you change the system type to a Power Induction Unit (which is a VAV) and
> you zero out the fan power, this might work.
>
> There is no induction ratio parameter then, but I have played around with
> that parameter in eQUEST and seen almost no impact from varying it.
>
> I am attempting to modeling an active chilled beam system served by a VAV
> DOAS right now, so if anyone else has comments on the Power Induction Unit
> approach, please let me know!
>
>
> Kendra Tupper, PE, LEED AP
> Senior Consultant
> Built Environment Team
>
> Rocky Mountain Institute | T 303-567-8641 | F 303-245-7213 |
> www.rmi.org
>
>
> On Thu, May 6, 2010 at 9:37 AM, Ellen Franconi <efranconi at rmi.org<http://us.mc656.mail.yahoo.com/mc/compose?to=efranconi@rmi.org>
> > wrote:
>
>> Vishnu,
>> I am not sure I completely follow what you did but perhaps you are not
>> aware that the induction unit system includes a central fan for pretreating
>> outside air delivered to the induction units. So if you used the "outside
>> air from sys" approach,the central fan of the induction unit would still be
>> modeled with its default parameters. Also, if you don't set the induction
>> ratio high enough (e.g. default is 3, max value is 10), you will get return
>> air mixing with your supply (e.g it will no longer be 100% OA), which will
>> make your supply air flow higher. This will increase your fan energy use as
>> well.
>>
>> I don't think the eQUEST documentation includes a description of the
>> induction unit system (TPIU or FPIU) but its relevant keywords can found in
>> the DOE2.1E BDL Summary. You could also insert the following commands in
>> your input file.
>>
>> DIAGNOSTICS DEFAULTS .. $ before the SYSTEM command and
>> DIAGNOSTICS CAUTIONS .. $ after the SYSTEM command
>>
>> Adding the above will show in the BDL file the value for all keywords not
>> explicitly listed but with default values being used.
>> Ellen
>>
>> On Wed, May 5, 2010 at 11:14 PM, Vishnuraj Nair <vishnu at kalpakrit.com<http://us.mc656.mail.yahoo.com/mc/compose?to=vishnu@kalpakrit.com>
>> > wrote:
>>
>>> Dear friends,
>>>
>>>
>>>
>>> I am modeling the active chilled beams system using an induction unit. I
>>> have created a separate treated outside air system (TOAS) from where the
>>> fresh air would be supplied to
>>>
>>> the induction unit. I have hard coded the fresh air requirement for each
>>> zone at the outdoor air CFM field under outside air tab as well as under
>>> design flow cfm field under air flow tab
>>>
>>> so that the only the fresh air requirement is supplied to the zone. The
>>> cooling will be done by chilled beams modeled as induction unit.
>>>
>>
>>
> when I see the simulation report the amount of fan energy consumed is huge
> which is nearly about 20% percent of the overall energy consumption.
>
> So then I zeroed out the fan energy i.e kW/CFM for fans =0 and only the
> TOAS has the fan energy but the fan energy consumption decreased very
> little.
>
> I have no other source in the model for which the fan energy could be
> accountable for.
>
>
>
> Can anyone please tell what can be the reason for this or if I am missing
> out on something?
>
> Am I modeling the system right? How is the fan energy for this system to be
> modeled?
>
> Vishnuraj Nair
>
> Kalpakrit Sustainable Environments Pvt. Ltd.
>
> New Delhi
>
> Tel: +91.124.4309490-92 Ext: 312 , Fax: +91.124.4309493
>
> E-mail : vishnu at kalpakrit.com<http://us.mc656.mail.yahoo.com/mc/compose?to=vishnu@kalpakrit.com>
>
> *Disclaimer: The information contained in this message is confidential and
> may be legally privileged. The message is intended solely for the
> addressee(s). If you are not the intended recipient, you are hereby notified
> that any use, dissemination, or reproduction is strictly prohibited and may
> be unlawful. If you are not the intended recipient, please contact the
> sender by return e-mail and destroy all copies of the original message. The
> views expressed in this e-mail message (including any attachments) are those
> of the individual sender except where the sender expressly, and with
> authority, states them to be the views of Kalpakrit or its group companies
> and the same shall be subject to the terms and conditions in governing
> contract in writing, if any. Kalpakrit or its group companies have all
> authority to check all emails being exchanged using the above address.*
>
>
>
> ü Please consider the environment before printing this email.
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG>
>
>
>
>
> --
> Ellen Franconi, PhD, LEED AP
> Senior Consultant, Built Environment Team
>
> Rocky Mountain Institute
> 1820 Folsom Street
> Boulder, CO 80302
> 303.567.8609 (Desk)
> 303.245.7213 (Fax)
>
> Rocky Mountain Institute drives the efficient and restorative use of
> resources, creating a world thriving, verdant, and secure, for all, for
> ever.
>
> http://www.rmi.org
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG>
>
>
>
> -----Inline Attachment Follows-----
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100506/078c83c8/attachment.htm>
More information about the Bldg-sim
mailing list