[Bldg-sim] ASHRAE 90.1 "HC" heat capacity

Nick Caton ncaton at smithboucher.com
Wed Mar 24 07:42:52 PDT 2010


I ran the exact same calc yesterday and came to the same
results/conclusion (using 4" brick and the 2001 Fundamentals...
spooky!).

 

My conclusion was any wall construction including 4"brick is a mass wall
by 90.1 definition, even if it should also use steel framing.

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Seth P.
Spangler
Sent: Wednesday, March 24, 2010 8:44 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 "HC" heat capacity

 

Hello,

 

ASHRAE defines a mass wall as a wall having a heat capacity (HC) of
greater than 7 BTU/ft2 * F but I have been unable to find this property
listed in tables of building materials. I am trying to calculate the
heat capacity of a CMU wall and would like to confirm that my
calculation methodology is correct.

 

Per ASHRAE 1997 Fundamentals:

*         8" concrete block - two cores filled with concrete (normal
weight) - ~130 lb/ft3

*         Thickness .67 ft

*         Specific Heat ~ 0.22 BTU/lb * F

 

Therefore NC =(130 lb/ft3 )*(.67 ft)*(0.22 BTU/lb * F)

 

NC=19.16

 

Using this methodology even a 4" brick wall has a HC greater than 7 (7.5
to be exact).

 

Thanks in advance.

 

Seth Spangler, LEED(r) AP 

Project Engineer

 

RMF Engineering, Inc 

Ph: (843) 971-9639 ext:1497

Fax: (843) 971-9641 

sspangle at rmf.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100324/23df492f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100324/23df492f/attachment.jpeg>


More information about the Bldg-sim mailing list