[Bldg-sim] thoughts on App G system type for mixed use building

Eurek, John S NWO John.S.Eurek at usace.army.mil
Wed Mar 10 13:27:06 PST 2010


To add my thoughts onto Kevin's

The whole building may need to be system 5, but they can be multiple system
5s.
	So one system type #5 for the office area, and a completely separate
system type #5 for the storage area and another for the manufacturing.  This
will make the return air for each system closer to the supply.  Using three
separate systems would also make your baseline more efficient making your
design improvement lower.

	I agree with your idea of modeling a cooling system but making the
set points extremely high and extremely low so they never turn on. I have
received this same advice on other projects.

	

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kevin Kyte
Sent: Wednesday, March 10, 2010 2:49 PM
To: James Hansen; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] thoughts on App G system type for mixed use building

James,

 

It has been awhile since I have really looked at 90.1-2007, but your space
type has no bearing on what the system type is going to be.  You just need to
know whether your building type is res or not, this should be whole building.
Seeing that you reference 2004 and assuming your project is 2.2 (also you
should be referencing the actual standard not the manual for finality), you
should be using system 5 or 6 due to the square footage.  I got jammed up on
the square footage vs. number of floors once myself.  I got reviewed on a job
where the building was one floor and 80k sqft but I had used system 3.  When
I changed to system 5 the savings doubled, I resubmitted and since the
project was on the cusp of silver to gold, they got gold instead of the
expected silver.  I am assuming everyone was just glad things worked out
there.

 

Secondly, I don't think whether the space is conditioned or not matters
either. G expects all spaces to be conditioned.  I say again, it has been
awhile since I have thoroughly looked at this standard and I know a few
people have quarks about the whole space conditioning expectations (just
trying to get some good discussion going) seeing as how us HVAC/energy guys
are so stuck on carbon-based realties.  But, in reality (and to answer your
question), the entire charade is all up to interpretation anyways :-)

 

 

________________________________

From: James Hansen [mailto:JHANSEN at ghtltd.com]
Sent: Wednesday, March 10, 2010 2:39 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] thoughts on App G system type for mixed use building

 

I can't find an addenda on this, but which publication is correct for
defining the baseline system of a non-residential building less than 3
stories?

 

The base 90.1-2004 document says that if the building is 3-stories or less
AND < 75,000 sq ft, System 3 and 4 are to be used.

The User's Manual, on the other hand, says "For smaller non-residential
buildings that are less than 75,000 ft2 (any height) OR less than three
stories (any area)"...the baseline system is PSZ (System 3 or 4)

 

Which is correct?

 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

 

From: James Hansen
Sent: Wednesday, March 10, 2010 12:45 PM
To: 'Gregg Liddick'; bldg-sim at lists.onebuilding.org
Subject: RE: thoughts on App G system type for mixed use building

 

Thanks Greg, but based on the heating density, I can't classify these as
semi-heated.

 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

 

From: Gregg Liddick [mailto:gliddick at theepstengroup.com]
Sent: Wednesday, March 10, 2010 11:21 AM
To: James Hansen; bldg-sim at lists.onebuilding.org
Subject: RE: thoughts on App G system type for mixed use building

 

Hi James,

 

It sounds like the storage and workshop area may be semi-heated as defined by
Section 3.  I'd recommend looking into that.  If the spaces are semi-heated
then they should be modeled only with heating in the baseline case and the
requirements of Table G3.1.10 don't apply.  It's also worth noting that if
the spaces are semi-heated they should be modeled with different envelope
values in the baseline case (based on the semi-heated in Table 5.5).

 

 

Best Regards,

 

Gregg Liddick, EIT, LEED(r) AP

 

The Epsten Group, Inc.

429 Edgewood Avenue

Atlanta GA 30312

Phone: 404-577-0370  ext. 102

Fax: 404-577-1739

www.theepstengroup.com <http://www.theepstengroup.com> 

 

Please consider the environment before printing this e-mail.

 

This transmission is intended exclusively for the individual or entity to
which it is addressed. This communication may contain information that is
confidential, proprietary, privileged or otherwise exempt from disclosure. If
you are not the named addressee, you are NOT authorized to read, print,
retain, copy or disseminate this communication, its attachments or any part
of them. If you have received this communication in error, please notify the
sender immediately and delete this communication from all computers. This
communication does not form any contractual obligation on behalf of the
sender, the sender's employer, or the employer's parent company, affiliates
or subsidiaries.

 

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Wednesday, March 10, 2010 11:02 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] thoughts on App G system type for mixed use building

 

I've got a 92,000 square foot Industrial building that I am modeling.  If you
went by Table G3.1.1A, the baseline system type would be System 5 - Packaged
VAV with reheat.

 

However, of the 92,000 square feet, approximately 16,000 sq ft is conditioned
to standard 75/72 degrees, while the remainder is a mixture of storage,
manufacturing, etc, and is heated to 55 and cooled to 120 (no actual cooling
in proposed model, but you've got to insert some sort of cooling system per
App G).

 

So I really have 16,000 sq ft that is fully conditioned, and 76,000 sq ft
that is only partially conditioned (ie the peak thermal load differs by 10
Btu/h-ft2).  

 

Any guesses how I configure this?

 

Do I have a packaged VAV system for the 76,000 sq ft of shop/storage and
isolate the 16,000 ft2 of real conditioned space as system 3 per the
Exception to G3.1.1?  

 

Or do I have a packaged VAV system for the 16,000 ft conditioned space and
isolate the 76,000 sq ft as system 3?

 

To further complicate things, since the 76,000 sq ft is split between storage
and manufacturing, where there is theoretically an operating schedule that
differs by 40 hours or more a week between these two different use types, do
I actually just end up with ALL system 3 even though the total net building
area is above the 75,000 sq ft cutoff where we're supposed to go to System 5?

 

I'm confused!  Any help would be appreciated.

 

To recap:

 

16,000 sq ft office, heated/cooled to 72/75

30,000 sq ft of storage with basically no operating hours per week,
heated/cooled to 50/120

36,000 sq ft of manufacturing / workshop area that is used approximately 50
hrs a week, heated/cooled to 50/120

 

Mixture of System 3 and System 5, or ALL system 3?

 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

 

________________________________

The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee.  It is the
property of GHT Limited.  Unauthorized use, disclosure or copying of this
communication or any part thereof is strictly prohibited and may be unlawful.
If you have received this communication in error, please notify me
immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments.  Thank you.

________________________________

The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee.  It is the
property of GHT Limited.  Unauthorized use, disclosure or copying of this
communication or any part thereof is strictly prohibited and may be unlawful.
If you have received this communication in error, please notify me
immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments.  Thank you.



More information about the Bldg-sim mailing list