[Bldg-sim] Bldg-sim Digest, Vol 28, Issue 4

Andrew Phelps Andrew.Phelps at larsonbinkley.com
Fri Mar 5 06:04:36 PST 2010


Caroline:

Good morning.  I'd agree with Bill. 

Per the definitions in section 3.2 of 90.1, a cooled space (and heated
space for your climate zone in particular) is defined as a space that
contains a cooling (heating) system with a sensible output exceeding 5
btu/sf.  Since you have no heating or cooling systems, I would classify
your space as unconditioned.  If it is unconditioned, the comment
regarding table G3.1.1(b) doesn't apply since it specifically mentions
conditioned spaces.

Andy


  Andy Phelps, PE - Mechanical Engineer
    	Larson Binkley, Inc.
	6363 College Blvd., Suite 400 Overland Park, KS 66211
      (T-direct) 913-383-5861 (T-main) 913-383-2621 (F) 913-383-2831







-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
bldg-sim-request at lists.onebuilding.org
Sent: Thursday, March 04, 2010 2:01 PM
To: bldg-sim at lists.onebuilding.org
Subject: Bldg-sim Digest, Vol 28, Issue 4




More information about the Bldg-sim mailing list