[Bldg-sim] Apendix G3.1.2.9
Gregg Liddick
gliddick at theepstengroup.com
Wed Mar 24 06:18:11 PDT 2010
Hi Kim,
I'm fairly certain that there's no specific guidance in Appendix G. What most people do is break it up so that it's proportional to the proposed case. For example if the baseline fan power is 34.5 kW and the actual parameters call for 20 kW supply and 10 kW return you would break the baseline case up into 23 kW supply and 11.5 kW return. I hope that helps.
Gregg Liddick, EIT, LEED(r) AP
The Epsten Group, Inc.
429 Edgewood Avenue
Atlanta GA 30312
Phone: 404-577-0370 ext. 102
Fax: 404-577-1739
www.theepstengroup.com<http://www.theepstengroup.com>
Please consider the environment before printing this e-mail.
This transmission is intended exclusively for the individual or entity to which it is addressed. This communication may contain information that is confidential, proprietary, privileged or otherwise exempt from disclosure. If you are not the named addressee, you are NOT authorized to read, print, retain, copy or disseminate this communication, its attachments or any part of them. If you have received this communication in error, please notify the sender immediately and delete this communication from all computers. This communication does not form any contractual obligation on behalf of the sender, the sender's employer, or the employer's parent company, affiliates or subsidiaries.
From: Kimberly Killian [mailto:Kimberly at NorthernArchitects.com]
Sent: Wednesday, March 24, 2010 7:36 AM
To: Gregg Liddick; syedf at progressiveae.com; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Apendix G3.1.2.9
Gregg,
Is there guidance on what portion of the Pfan goes to each? What percentage goes to supply, what percentage to return, etc?
Kimberly Killian
Northern Architects, Inc.
207 King Street Suite 3
Burlington VT 05401
T: 802-658-1953
F: 802-658-2975
________________________________
Original message
From: "Gregg Liddick"
To: syedf at progressiveae.com; bldg-sim at lists.onebuilding.org
Received: 3/23/2010 5:24:39 PM
Subject: Re: [Bldg-sim] Apendix G3.1.2.9
No, you use only the fan supply cfm to calculate the total fan power, then cut that fan power up into supply, return, etc.
Best Regards,
Gregg Liddick, EIT, LEED(r) AP
The Epsten Group, Inc.
429 Edgewood Avenue
Atlanta GA 30312
Phone: 404-577-0370 ext. 102
Fax: 404-577-1739
www.theepstengroup.com<http://www.theepstengroup.com/>
Please consider the environment before printing this e-mail.
This transmission is intended exclusively for the individual or entity to which it is addressed. This communication may contain information that is confidential, proprietary, privileged or otherwise exempt from disclosure. If you are not the named addressee, you are NOT authorized to read, print, retain, copy or disseminate this communication, its attachments or any part of them. If you have received this communication in error, please notify the sender immediately and delete this communication from all computers. This communication does not form any contractual obligation on behalf of the sender, the sender's employer, or the employer's parent company, affiliates or subsidiaries.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Fareed Syed
Sent: Tuesday, March 23, 2010 5:11 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Apendix G3.1.2.9
Hello All,
I am trying to understand the stated appendix for the baseline model.
When I am calculating the Pfan for a system, do I need add up supply, return, system and room exhaust cfm's?
I got this comment from GBCI: "Revise the sum of the supply, return, exhaust, and relief fans for each HVAC system to be equal to the volume calculated in G3.1.2.8 and power calculated in G3.1.2.9 (where CFM refers to supply air volume)."
Please let me know your input on how to calculate Pfan.
Thanks,
Fareed Syed EIT, LEED(r) AP
Mechanical Engineer
[cid:image001.png at 01CACB32.CC7E6800]
1811 4 Mile Rd NE
Grand Rapids, MI 49525
Phone: 616.361.2664 ext. 3247
Direct: 616.447.3447
Fax: 616.361.1493
syedf at progressiveae.com<mailto:syedf at progressiveae.com>
www.progressiveae.com<http://www.progressiveae.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100324/81848d59/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 7502 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100324/81848d59/attachment.png>
More information about the Bldg-sim
mailing list