[Bldg-sim] Model External Shading Devices for LEED compliance

W. Peter Anderson panderson at jpengineer.com
Mon Mar 22 07:41:31 PDT 2010


Greetings-
Hisham makes a good point, why would you want to?  But more specifically, Table G3.1 - 5 c states shading shall NOT be modeled, so there really is no debate.

Regards,
W. Peter Anderson, P.E
JP Engineering
41 Mechanic Street
Windsor, CT 06095
Ph: 860/688-5223
Fax: 860/688-5269
  ----- Original Message ----- 
  From: Hisham Ahmad 
  To: Lizzy Guhl 
  Cc: bldg-sim at lists.onebuilding.org 
  Sent: Monday, March 22, 2010 8:43 AM
  Subject: Re: [Bldg-sim] Model External Shading Devices for LEED compliance


  Hi,

  The baseline has to be modeled as per G3.1.5 which does not require shading devices to be modeled. Why would you want to model them in the baseline ?? This will only compromise your energy savings.


  On 22 March 2010 18:01, Lizzy Guhl <lizzy.guhl at energyarq.com> wrote:

    Thanks for the fast reply. But it is possible, anyway, to model the baseline building with external shading devices, right?



    De: Hisham Ahmad [mailto:hisham at edsglobal.com] 
    Enviado el: Lunes, 22 de Marzo de 2010 7:58
    Para: Lizzy Guhl
    CC: bldg-sim at lists.onebuilding.org
    Asunto: Re: [Bldg-sim] Model External Shading Devices for LEED compliance



    Hi,

    Appendix G allows you to claim credit for shading designs/devices. Therefore, the baseline building is not required to have shading devices/projections.

    On 22 March 2010 17:22, Lizzy Guhl <lizzy.guhl at energyarq.com> wrote:

    Dear All,



    I am new to Leed compliance simulations and I would like to know how to model external shading devices in the proposed and baseline building. Appendix G, Table G3.1 – 5. Building Envelope, is clear about permanent shading devices being allowed for the proposed building. But what about the baseline building? Do you model the external shading devices in the baseline building as well?



    I´d appreciate any help on the matter.



    Regards,

    Lizzy





    LIZZY GUHL
    Dipl. Ing. (FH) Mechanical Engineering | Sustainable Design Consultant



    ENERGY A R Q
    Sustainability | Energy | Building Simulations | LEED®
    Member of the United States Green Building Council (USGBC)
    Chile: Juan Bautista Pastene 3120, Vitacura, Santiago | Tel. +56 2 9813142
    USA: 31 Willard St., Cambridge, MA | Tel. +1 617 710 2360
    www.energyarq.com



    P  Consider the environment before printing this email





    __________ Información de ESET NOD32 Antivirus, versión de la base de firmas de virus 4964 (20100322) __________

    ESET NOD32 Antivirus ha comprobado este mensaje.

    http://www.eset.com


    _______________________________________________
    Bldg-sim mailing list
    http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
    To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG




    -- 

    Regards
    Hisham Ahmad

    Energy Analyst
    Environmental Design Solutions Pvt Ltd.
    www.edsglobal.com
    New Delhi, India
    +91-9873065488




  -- 

  Regards
  Hisham Ahmad

  Energy Analyst
  Environmental Design Solutions Pvt Ltd.
  www.edsglobal.com
  New Delhi, India
  +91-9873065488



------------------------------------------------------------------------------


  _______________________________________________
  Bldg-sim mailing list
  http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
  To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100322/55507f96/attachment.htm>


More information about the Bldg-sim mailing list