[Bldg-sim] Equest:Variation in pumping energy for Baseline system 8
Gaurav Mehta
gmehta75 at gmail.com
Thu Mar 18 00:18:52 PDT 2010
Vishnuraj,
If I get your question correct, then you are wondering why is your project 1 with 2 chillers showing less pump energy than Project 2 which has 1 chiller, the other parameters being the same with a slight difference in areas of both the project. Is this correct?
If I got your question correct, which I think I do, as I was able to duplicate the same behavior in a test project. I changed only the number of chillers and simulated in two locations.....( I know you might think I have got a lot of time on my hand..... but believe it or not this is a break from EnergyPro....anyway....)
Here are the results:
Project with 2 chillers: Less Pump Energy
Project with 1 chiller: More Pump Energy
However, I can offer only a partial answer. May be somebody reading this may have the complete answer.
The answer to your question is in the CW loop pump. The project with 2 chillers, shows that the CW loop pump runs in lower part load ranges than the project with 1 chiller (see the PS-H Report). A Pump sized for peak load conditions would use less energy when running at part load. Therefore, the project with 2 chillers uses less pump energy than the project with 1 chiller.
Hope this helps.
Best regards,
Gaurav Mehta
Sustainable Building Analyst
Stantec
From: Vishnuraj Nair
Sent: Wednesday, March 17, 2010 04:26
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Equest:Variation in pumping energy for Baseline system 8
Dear friends,
I am working on two projects of core and shell where the baseline system is system 8 i.e VAV with fan powered boxes.
There are two different building which are very similar in nature (not same) and situated at same location.
However there are differences in the way the two models are behaving.
I have shown the breakdown of different end uses as a percentage of overall baseline energy consumption
Project 1
Plug loads: 25.5 %
Interior Lighting: 16%
Cooling energy: 28.7%
Fan energy: 21%
Pumps: 6.3 %
Space heating: 0.1%
Domestic hot water + Exterior Lighting: 1.3 %
Project 2
Plug loads: 24 %
Interior lighting: 15%
Cooling energy: 18%
Fan energy: 25%
Pumps: 15 %
Space heating: 0.3%
Domestic hot water + Exterior Lighting: 1.3%
It can be seen that the energy consumed due to plug loads and interior lighting as a percentage of baseline are all most equal in both the cases.
Can anyone suggest possible explanation or give hints as to why the pumping energy as a percentage of baseline has more than doubled in the
second case given that the characteristics of chiller, condenser and pump remain same ,given it is the baseline case.
One difference is that the first project uses two chillers as it has conditioned area more than 1, 20,000 sq ft while the second project has only
one chiller ,its conditioned area being less than 1, 20,000
Vishnuraj Nair
Kalpakrit Sustainable Environments Pvt. Ltd.
New Delhi
Tel: +91.124.4309490-92 Ext: 312 , Fax: +91.124.4309493
E-mail : vishnu at kalpakrit.com
Disclaimer: The information contained in this message is confidential and may be legally privileged. The message is intended solely for the addressee(s). If you are not the intended recipient, you are hereby notified that any use, dissemination, or reproduction is strictly prohibited and may be unlawful. If you are not the intended recipient, please contact the sender by return e-mail and destroy all copies of the original message. The views expressed in this e-mail message (including any attachments) are those of the individual sender except where the sender expressly, and with authority, states them to be the views of Kalpakrit or its group companies and the same shall be subject to the terms and conditions in governing contract in writing, if any. Kalpakrit or its group companies have all authority to check all emails being exchanged using the above address.
ü Please consider the environment before printing this email.
--------------------------------------------------------------------------------
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100318/b1e53d49/attachment.htm>
More information about the Bldg-sim
mailing list