[Bldg-sim] Equest:Variation in pumping energy for Baseline system 8
Vishnuraj Nair
vishnu at kalpakrit.com
Wed Mar 17 04:26:51 PDT 2010
Dear friends,
I am working on two projects of core and shell where the baseline system is
system 8 i.e VAV with fan powered boxes.
There are two different building which are very similar in nature (not same)
and situated at same location.
However there are differences in the way the two models are behaving.
I have shown the breakdown of different end uses as a percentage of overall
baseline energy consumption
Project 1
Plug loads: 25.5 %
Interior Lighting: 16%
Cooling energy: 28.7%
Fan energy: 21%
Pumps: 6.3 %
Space heating: 0.1%
Domestic hot water + Exterior Lighting: 1.3 %
Project 2
Plug loads: 24 %
Interior lighting: 15%
Cooling energy: 18%
Fan energy: 25%
Pumps: 15 %
Space heating: 0.3%
Domestic hot water + Exterior Lighting: 1.3%
It can be seen that the energy consumed due to plug loads and interior
lighting as a percentage of baseline are all most equal in both the cases.
Can anyone suggest possible explanation or give hints as to why the pumping
energy as a percentage of baseline has more than doubled in the
second case given that the characteristics of chiller, condenser and pump
remain same ,given it is the baseline case.
One difference is that the first project uses two chillers as it has
conditioned area more than 1, 20,000 sq ft while the second project has only
one chiller ,its conditioned area being less than 1, 20,000
Vishnuraj Nair
Kalpakrit Sustainable Environments Pvt. Ltd.
New Delhi
Tel: +91.124.4309490-92 Ext: 312 , Fax: +91.124.4309493
E-mail : <mailto:vishnu at kalpakrit.com> vishnu at kalpakrit.com
Disclaimer: The information contained in this message is confidential and
may be legally privileged. The message is intended solely for the
addressee(s). If you are not the intended recipient, you are hereby notified
that any use, dissemination, or reproduction is strictly prohibited and may
be unlawful. If you are not the intended recipient, please contact the
sender by return e-mail and destroy all copies of the original message. The
views expressed in this e-mail message (including any attachments) are those
of the individual sender except where the sender expressly, and with
authority, states them to be the views of Kalpakrit or its group companies
and the same shall be subject to the terms and conditions in governing
contract in writing, if any. Kalpakrit or its group companies have all
authority to check all emails being exchanged using the above address.
* Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100317/64a2cb55/attachment.htm>
More information about the Bldg-sim
mailing list