The appropriate section happens to be right in front of me - assuming
you have task lights defined in the construction documents (plans/specs)
being reviewed, it looks to me that your USGBC reviewer is correct, but
not telling you the whole story...
90.1-2004, Appendix G, Table G3.1, Section 6. "Lighting" (d):
"Lighting system power shall include all lighting system components
shown or provided for on the plans (including lamps and ballasts and
task and furniture-mounted fixtures)."
The following exception for multifamily dwellings and hotel/motel guest
rooms makes a distinction regarding cord + receptacle task lights:
"Exception: For... spaces in which lighting systems are connected via
receptacles and are not shown or provided for on building plans, assume
identical lighting power for the proposed and baseline building designs
in the simulations, but exclude these loads when calculating the
baseline building performance and proposed building performance."
Falling back to the glossary definition for performance (cost), that
means if you are modeling the task lights, add their wattage identically
to the baseline and proposed model LPD's to model the internal load
contributions, but then subtract the cost of the energy to operate those
fixtures from the final costs you arrive at.
In summary, you should model the task lights as internal loads, but not
the cost of operating them. That's my take anyway =),
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Priya
Premchandran
Sent: Friday, March 12, 2010 11:16 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1-2004 and task lights
Hello Listserv members,
I just received a question from GBCI on a LEED CI project related to
lighting power density. It was my understanding that per ASHRAE
90.1-2004 std. plugged in task lights are exempted from the overall
lighting power density calculations. However, our review came back
saying that task lights should be included in the overall calculations.
Is this true? Has the standard changed recently?
Any input is greatly appreciated.
Thanks,
Priya
Priya Premchandran, Int'l Associate AIA, LEED(r) AP
www.serapdx.com <http://www.serapdx.com>
503.445.7368
P Please consider the environmental impact before printing this email
________________________________
DISCLAIMER:
This message and any attachments are intended for the sole use of the
individual or entity to whom it is addressed. It may contain information
that
is privileged, confidential, and / or exempt from disclosure under
applicable
law. If you are not the intended recipient, you are hereby notified that
you
may not use, copy, disclose, or distribute this message or any
information
contained within, including any attachments, to anyone. If you have
received
this message in error, please immediately advise the sender and
permanently
delete the message and any attachments and destroy any printouts made.
Although we have taken steps to ensure that our e-mail and attachments
are
free
from viruses, the recipients should also ensure that they are virus
free.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100312/6b70b80d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100312/6b70b80d/attachment.jpeg>
More information about the Bldg-sim
mailing list