You are to increase the cooling/heating coil capacities as required by
ASHRAE Appendix G. However, the over sizing is for coil capacity only -
the airflow rate should be sized at 100% of what your energy modeling
program calculates as being required to meet the space load.
Thanks
Seth Spangler, LEED(r) AP
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V
Dirkes II, PE
Sent: Wednesday, June 23, 2010 7:16 PM
To: 'Vinay Devanathan'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] sizing for baseline case acc to App. G
Dear Vinay,
I'm not sure of the rationale for the ASHRAE 90.1 oversizing
requirements, however here are my thoughts:
* I think the principal engineering rationale for oversizing is
to allow a building to reach its setpoint temperature quickly after a
period of inactivity. As an example, if a building is inactive during a
holiday and the temperature is allowed to float several degrees lower
(in winter), the additional 25% heating capacity will enable faster
return to the normal setpoint temperature. Steam heating systems can
need even more capacity for proper warmup capacity.
* Oversizing is also a common practice as a "safety factor".
Most load calculation software even has a separate input for adding this
"safety factor".
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay
Devanathan
Sent: Wednesday, June 23, 2010 10:00 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] sizing for baseline case acc to App. G
Hello All,
Just to clarify a point -
What does the oversizing of capacities by 15% for cooling and 25% for
heating exactly mean? Do we only size the cooling and heating capacity
or also increase the airflow rate corresponding to the oversizing?
Thank you.