[Bldg-sim] Window performance with frames
mark dewsbury
Mark.Dewsbury at utas.edu.au
Thu Jul 22 00:32:53 PDT 2010
Dear Alex,
I work in the HER validation field , so we need to know that we are
modelling the right fabric matrix (framing factor and windows included). The
software available in Australia only has the NFRC type table for selection,
which is unsuitable for us. The get around the problem we can modify the
data in the softwares scratch file. This is a file the software creates
post data entry before simulation. We open this file and modify lots of
parameters based on as-built observations.
Once you start playing at this level, you actually create as many windows as
you wish. You just need & checking with the data entry. We mainly modify the
framing ratios of a suitable NFRC window to match what is really in the
wall. It is laborious, so I do believe that we need a parametric model
within the HER software which can ultimately make the changes for us. The
only other addition would then be a mullions tool to nominate how many
vertical and horizontal mullions.
We are to discuss this in Australia when I finish my current windowless
project. But I have been advising another researcher with a windowed
project.
Mark Dewsbury
Centre for Sustainable Architecture with Wood
School of Architecture
University of Tasmania
Locked Bag 1324
Launceston 7250
ph: 03 6324 4089
mob: 0417 290 807
fax: 03 6324 4088
e: mark.dewsbury at utas.edu.au
_____
From: Alex Krickx [mailto:akrickx at seriousmaterials.com]
Sent: Wednesday, 21 July 2010 3:22 AM
To: mark dewsbury; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Window performance with frames
Hi Mark,
I agree with the point you make, but I want to expand the conversation a
bit. Specifically, I aim to discuss the difference between how to use NFRC
values and how to input values into energy modeling software.
The NFRC value should be accurate for a window of the NFRC standard size. So
a standard sized 1200mm x 1500mm fixed window will have a certain U-factor,
SHGC and VT as part of its NFRC rating. But a different size will certainly
have different performance values. I think NFRC is very useful in comparing
Window A to Window B in a standard size, but you are right: once youve
selected Window A we need to make sure that we have the right performance
parameters for that sized window.
Ive been working on some projects that are aiming to be Passive House
certified in which case they DO need to know how performance varies with
size. Weve worked out some formulas to calculate the full frame performance
(only for U-factor at this point) on a range of our products. Its tricky
because you need to know the U-factor of each component (edge of glass
against each part of the frame, each part of the frame, and COG) as well as
the areas of each of those components which of course vary with different
sized windows.
Im not sure what other manufacturers are doing to be able to provide this,
but we have some of our product lines in a format that we can provide an
NFRC-grade value for a non-NFRC sized window.
If you want to see the calculations, you can follow this link:
http://index.seriouswindows.com/passive-house.html and click Download
SeriousWindows for Passive House at the bottom of the page or click here:
http://index.seriouswindows.com/document-library/func-startdown/90/.
The document describes how the window is broken into different sections and
includes all the necessary info needed to calculate full frame performance.
The last thing Id like to add: It is probably simpler to upload WINDOW5
data (I know eQUEST can import COG spectral data), specify your window size
in the modeling software and specify your frame U-factor. Your software
should take all that data and calculate what the full-frame data is pretty
accurately.
If anyone has any questions about this, feel free to contact me: generating
these formulas took quite a bit of time and Id be happy to share my
learning.
Regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
email_sig
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential. If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of mark dewsbury
Sent: Monday, July 19, 2010 4:45 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Dear All,
Are we talking about the assessment for simple regulatory approval or are we
talking about what a window really is. We have found dramatic variations
between NFRC values and what actually goes into a building. I will not go
into differences in measured infiltration rates as that is too random but
the window framing factor is fairly parametric.
The NFRC tables work on a sample window size (lest say 900mm x 1200mm). This
is quite a small window when compared to most installations but;
- For windows smaller than the sample size the frame to galls
factor is much higher,
- Conversely for large format windows commonly used in residential
& commercial projects the framing factor is much less. In some test cases we
have calculated framing factors changing from 18% to 8% or even less.
Depending on Glass system and framing system this can create some
interesting changes to thermal simulation results. One of my colleagues will
hopefully publish something on this late 2010 or early 2011.
Mark Dewsbury
Centre for Sustainable Architecture with Wood
School of Architecture
University of Tasmania
Locked Bag 1324
Launceston 7250
ph: 03 6324 4089
mob: 0417 290 807
fax: 03 6324 4088
e: mark.dewsbury at utas.edu.au
_____
From: Alex Krickx [mailto:akrickx at seriousmaterials.com]
Sent: Saturday, 17 July 2010 5:05 AM
To: Nick Caton; D. Charlie Curcija; Andy Hoover; Otto Schwieterman;
bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Hi Nick,
I think I know the answer to some of your questions, for some others Im
happy to share my thoughts, and for the remainder I have no clue.
I have always assumed that for the DOE-2 Glass Library that those files have
Window5 report files behind them i.e. theyre not just single values for
U, SHGC and VT. I could be mistaken though.
Skipping number 2
I believe that Window5 is the same thing as WINDOW (technically, I think it
is called WINDOW5 and there is/soon will be WINDOW6).
Lastly Ive looked into some detail at how full frame U-factors are
calculated and how they vary by size. So as a brief tangent, I thought I
would look at whether SHGC varies by size too. I found that if a window had,
say 0.5 SHGC COG and the window was 90% glass, 10% frame (by area) the
resulting full frame SHGC was GREATER than (90%)*(0.5 SHGC). This means to
me that the frame has some non-zero SHGC contribution. Granted, it was small
(if I remember correctly on the order of 0.1) but still non-zero!!! In my
head I assumed that the frame would reflect additional heat through the
window into the space that may not be correct, but it made sense with my
results. I havent looked at VT that closely but I would assume the same is
true that the frame adds some small VT to the whole unit.
Regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
email_sig
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential. If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Friday, July 16, 2010 10:27 AM
To: D. Charlie Curcija; Andy Hoover; Alex Krickx; Otto Schwieterman;
bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Window performance with frames
Mr. Curcija and everyone:
If I may be so bold as to ask some dumb questions,
- Im an individual who regularly relies on the DOE2 Glass library
(a large excel file attached to any eQuest installation) to find window
constructions whose NFRC framed U-value, visible transmittance, and SHGC/SC
values best match those prescriptive values given for actual design models
and for 90.1 baseline models. Am I to understand all of my past models have
a 10% to 100% error with regard to the modeled behavior of the glazing?
Please explain!
- It sounds like the use of Window5 is pretty popular, and this
ability to export a file which can be used by DOE2 has me intrigued has
NFRC or any other body decided to make representative report files to match
90.1s baseline envelope requirements to encourage this procedure for
comparative studies?
- Is Window5 the same thing as WINDOW?
- Furthering Ottos original question, my reaction to a reviewer
requiring VLT including the frame would be to first roll my eyes and then
explain the frame has a VLT of zero, and is modeled distinctly from the
glazing which has a VLT of ##%
am I misunderstanding the request there?
Thanks!
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of D. Charlie
Curcija
Sent: Friday, July 16, 2010 9:16 AM
To: 'Andy Hoover'; 'Alex Krickx'; 'Otto Schwieterman';
bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Important thing to remember with windows is that the real number is the one
that account for actual size and that takes into account angle dependent
properties of glazing. In most cases, single performance indices at
standard conditions are used (i.e., U-factor, SHGC, and VT at normal
incidence and standard environmental conditions) in an energy model of a
building, which can produce errors anywhere from 10% to a 100%!! The
correct procedure is to either specify correct configuration and size of the
product, with glazing specified layer by layer (possible in EnergyPlus) or
use what is called DOE2 or EnergyPlus reports from WINDOW program (DOE2
report is used in DOE2 simulation program and E+ report is used in E+
simulation program). This is the only way to fully account for changes in
size, angular properties of glazing and actual weather conditions.
NFRC (National Fenestration Rating Council) has started to provide DOE2 and
E+ report files in their new CMAST certification system, however number of
products available is still relatively small and is limited to commercial
projects. EnergyPlus has also implemented in version 5.0 option to specify
standard numbers at standard conditions (like the ones available from
http://search.nfrc.org/search/searchDefault.aspx) and E+ uses then internal
algorithms to provide glazing angular information and correction for actual
conditions. While it is best to model specific configurations for a window
in THERM and WINDOW program (THERM is required to model frames and edge of
glazing), this is not something that average user will be able to do, so
getting whole product information from the NFRC web site and using E+ option
to convert this data to something resembling real performance is still the
best and easiest way to get actual information. For commercial products
http://cmast.nfrc.org provides full information that does not need any
simplifications or corrections.
Our energy simulation tools DesignBuilder and EFEN use EnergyPlus simulation
engine, with the full range of options mentioned above and also provide
hundreds of predefined fenestration products that can be matched to your
actual product.
D. Charlie Curcija
DesignBuilder Software
16 Bridge St.
Millers Falls, MA 01349
Tel: (413) 256-4647
Fax: (413) 256-4823
cell: (413) 575-3487
email: <mailto:curcija at designbuildersoftware.com>
curcija at designbuildersoftware.com
web: <http://www.designbuildersoftware.com/>
http://www.designbuildersoftware.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Andy Hoover
Sent: Friday, July 16, 2010 9:01 AM
To: 'Alex Krickx'; 'Otto Schwieterman'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Hey all:
We do not know Alex at all but completely support his position that it is
the entire assembly/full frame in use that counts. We are a building
envelope consultancy and deal principally in the built market and see this
issue all of the time where the performance of window, storefront and
curtain wall units is dramatically different than that calculated or
provided. As a matter of fact, it is the unfortunate norm. At the end of
the day it is about actual in use performance and that performance versus
what was calculated. I will stay away from installation difference in this
one :-).
Anyway, we do agree with and have seen the truth to his assessment of frame
differences. It is only the performance of the entire assembly, at every
level of a structure as a whole, that counts in the real world.
Thanks and take care,
Andy
Andy Hoover
Principal
The BEST Consultant, Inc.
Cell: 678-793-1159
Office: 678-200-7648
Fax: 678-827-0574
Email: andyhoover at thebestconsultant.com
Web: www.thebestconsultant.com
LEGAL DISCLAIMER
The information transmitted is intended solely for the individual or entity
to which it is addressed and may contain confidential and/or privileged
material. Any review, retransmission, dissemination or other use of or
taking action in reliance upon this information by persons or entities other
than the intended recipient is prohibited. If you have received this email
in error please contact the sender and delete the material from any
computer.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx
Sent: Wednesday, July 14, 2010 4:57 PM
To: Otto Schwieterman; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Hi Otto,
Serious Materials provides full frame performance data here:
http://index.seriouswindows.com/document-library/Datasheets/. I have also
have some of our commercial packages modeled in curtainwall and storefront
framing systems that I can provide upon request.
Firstly let me say that Window5 is a great tool I use it often and love
it. The only thing I would advise is that there can be a wide distribution
in frame U-factors. The default U-factor for a thermally broken aluminum
(TBA) frame in Window 5 is U-1.0. Using THERM and Window5 Ive seen TBA
frame U-factors vary from as low as 0.8 to as high as 1.5. The resultant
full-frame U-factor using these 2 differing TBA frames (and the same glass
package) is: 0.29 (R-3.4) for the poorer performing frame, and 0.22 (R-4.5)
for the better frame.
I would say that putting either of those full frame u-factors in your energy
model will yield pretty different results.
I think its really important that we, as simulators and modelers, look at
full-frame performance because this is the system that will be installed in
the building. Center-of-Glass data can be useful comparing two different
glass packages, but at the end of the day, its a framed system that will be
installed and a framed system that should be analyzed. My 2¢.
Regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
email_sig
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential. If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Wednesday, July 14, 2010 1:10 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Window performance with frames
Does anyone know of a window manufacturer web site that has literature on
its windows including the frame? I am using Trace 700 for EA Credit 1 and
the reviewer asked for manufacturer data sheets for window performance
values (U-value, VLT and SHGC) including the frame.
Your help is appreciated,
Otto
____________________________________________________________________________
____________
Fanning/Howey Associates, Inc. intends to send this transmission (including
any attachments) only to the
designated individual or entity. If you received this message in error,
please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no
viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our authorization,
verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100722/e4e63f09/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100722/e4e63f09/attachment.jpg>