[Bldg-sim] eQuest Model - VAV System gas savings

Shekhar, Diwanshu diwanshu.shekhar at lmco.com
Wed Jul 21 09:26:11 PDT 2010


Bhaskar,
All I can think of is tweaking the min variable air volume. Generally, the min air volume in the VAV system is 30%.
FYI: Oregon building code now has VAV min and max in the heating mode, i.e., 30% to 50% instead of constant 30%.

-Diwanshu

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vempati, Bhaskar
Sent: Monday, July 19, 2010 4:29 PM
To: bldg-sim at lists.onebuilding.org
Subject: EXTERNAL: [Bldg-sim] eQuest Model - VAV System gas savings

When I  modeled a measure, conversion of constant volume (or single zone reheat system) to variable air volume system with VFD fans in eQuest,  gas consumption is being reduced by 70 to 80% (i.e.,savings are 70 to 80%). I don't think this is true. Could any of you please help me on fixing this issue?

Thanks,
Bhaskar
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100721/4fb90dd9/attachment.htm>


More information about the Bldg-sim mailing list