[Bldg-sim] Window performance with frames
D. Charlie Curcija
curcija at designbuildersoftware.com
Fri Jul 16 14:21:07 PDT 2010
Alex,
Frame VLT is 0, unless it is made of transparent material of some sort.
Frame SHGC is NOT 0, because portion of the heat is absorbed by the frame
and re-directed to inside. The more conducting the frame the higher the
frame SHGC and vice versa
Charlie
From: Alex Krickx [mailto:akrickx at seriousmaterials.com]
Sent: Friday, July 16, 2010 3:05 PM
To: Nick Caton; D. Charlie Curcija; Andy Hoover; Otto Schwieterman;
bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Window performance with frames
Hi Nick,
I think I know the answer to some of your questions, for some others Im
happy to share my thoughts, and for the remainder I have no clue.
I have always assumed that for the DOE-2 Glass Library that those files have
Window5 report files behind them i.e. theyre not just single values for
U, SHGC and VT. I could be mistaken though.
Skipping number 2
I believe that Window5 is the same thing as WINDOW (technically, I think it
is called WINDOW5 and there is/soon will be WINDOW6).
Lastly Ive looked into some detail at how full frame U-factors are
calculated and how they vary by size. So as a brief tangent, I thought I
would look at whether SHGC varies by size too. I found that if a window had,
say 0.5 SHGC COG and the window was 90% glass, 10% frame (by area) the
resulting full frame SHGC was GREATER than (90%)*(0.5 SHGC). This means to
me that the frame has some non-zero SHGC contribution. Granted, it was small
(if I remember correctly on the order of 0.1) but still non-zero!!! In my
head I assumed that the frame would reflect additional heat through the
window into the space that may not be correct, but it made sense with my
results. I havent looked at VT that closely but I would assume the same is
true that the frame adds some small VT to the whole unit.
Regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
email_sig
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential. If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Friday, July 16, 2010 10:27 AM
To: D. Charlie Curcija; Andy Hoover; Alex Krickx; Otto Schwieterman;
bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Window performance with frames
Mr. Curcija and everyone:
If I may be so bold as to ask some dumb questions,
- Im an individual who regularly relies on the DOE2 Glass library
(a large excel file attached to any eQuest installation) to find window
constructions whose NFRC framed U-value, visible transmittance, and SHGC/SC
values best match those prescriptive values given for actual design models
and for 90.1 baseline models. Am I to understand all of my past models have
a 10% to 100% error with regard to the modeled behavior of the glazing?
Please explain!
- It sounds like the use of Window5 is pretty popular, and this
ability to export a file which can be used by DOE2 has me intrigued has
NFRC or any other body decided to make representative report files to match
90.1s baseline envelope requirements to encourage this procedure for
comparative studies?
- Is Window5 the same thing as WINDOW?
- Furthering Ottos original question, my reaction to a reviewer
requiring VLT including the frame would be to first roll my eyes and then
explain the frame has a VLT of zero, and is modeled distinctly from the
glazing which has a VLT of ##%
am I misunderstanding the request there?
Thanks!
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of D. Charlie
Curcija
Sent: Friday, July 16, 2010 9:16 AM
To: 'Andy Hoover'; 'Alex Krickx'; 'Otto Schwieterman';
bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Important thing to remember with windows is that the real number is the one
that account for actual size and that takes into account angle dependent
properties of glazing. In most cases, single performance indices at
standard conditions are used (i.e., U-factor, SHGC, and VT at normal
incidence and standard environmental conditions) in an energy model of a
building, which can produce errors anywhere from 10% to a 100%!! The
correct procedure is to either specify correct configuration and size of the
product, with glazing specified layer by layer (possible in EnergyPlus) or
use what is called DOE2 or EnergyPlus reports from WINDOW program (DOE2
report is used in DOE2 simulation program and E+ report is used in E+
simulation program). This is the only way to fully account for changes in
size, angular properties of glazing and actual weather conditions.
NFRC (National Fenestration Rating Council) has started to provide DOE2 and
E+ report files in their new CMAST certification system, however number of
products available is still relatively small and is limited to commercial
projects. EnergyPlus has also implemented in version 5.0 option to specify
standard numbers at standard conditions (like the ones available from
http://search.nfrc.org/search/searchDefault.aspx) and E+ uses then internal
algorithms to provide glazing angular information and correction for actual
conditions. While it is best to model specific configurations for a window
in THERM and WINDOW program (THERM is required to model frames and edge of
glazing), this is not something that average user will be able to do, so
getting whole product information from the NFRC web site and using E+ option
to convert this data to something resembling real performance is still the
best and easiest way to get actual information. For commercial products
http://cmast.nfrc.org provides full information that does not need any
simplifications or corrections.
Our energy simulation tools DesignBuilder and EFEN use EnergyPlus simulation
engine, with the full range of options mentioned above and also provide
hundreds of predefined fenestration products that can be matched to your
actual product.
D. Charlie Curcija
DesignBuilder Software
16 Bridge St.
Millers Falls, MA 01349
Tel: (413) 256-4647
Fax: (413) 256-4823
cell: (413) 575-3487
email: <mailto:curcija at designbuildersoftware.com>
curcija at designbuildersoftware.com
web: <http://www.designbuildersoftware.com/>
http://www.designbuildersoftware.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Andy Hoover
Sent: Friday, July 16, 2010 9:01 AM
To: 'Alex Krickx'; 'Otto Schwieterman'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Hey all:
We do not know Alex at all but completely support his position that it is
the entire assembly/full frame in use that counts. We are a building
envelope consultancy and deal principally in the built market and see this
issue all of the time where the performance of window, storefront and
curtain wall units is dramatically different than that calculated or
provided. As a matter of fact, it is the unfortunate norm. At the end of
the day it is about actual in use performance and that performance versus
what was calculated. I will stay away from installation difference in this
one J.
Anyway, we do agree with and have seen the truth to his assessment of frame
differences. It is only the performance of the entire assembly, at every
level of a structure as a whole, that counts in the real world.
Thanks and take care,
Andy
Andy Hoover
Principal
The BEST Consultant, Inc.
Cell: 678-793-1159
Office: 678-200-7648
Fax: 678-827-0574
Email: andyhoover at thebestconsultant.com
Web: www.thebestconsultant.com
LEGAL DISCLAIMER
The information transmitted is intended solely for the individual or entity
to which it is addressed and may contain confidential and/or privileged
material. Any review, retransmission, dissemination or other use of or
taking action in reliance upon this information by persons or entities other
than the intended recipient is prohibited. If you have received this email
in error please contact the sender and delete the material from any
computer.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx
Sent: Wednesday, July 14, 2010 4:57 PM
To: Otto Schwieterman; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Hi Otto,
Serious Materials provides full frame performance data here:
http://index.seriouswindows.com/document-library/Datasheets/. I have also
have some of our commercial packages modeled in curtainwall and storefront
framing systems that I can provide upon request.
Firstly let me say that Window5 is a great tool I use it often and love
it. The only thing I would advise is that there can be a wide distribution
in frame U-factors. The default U-factor for a thermally broken aluminum
(TBA) frame in Window 5 is U-1.0. Using THERM and Window5 Ive seen TBA
frame U-factors vary from as low as 0.8 to as high as 1.5. The resultant
full-frame U-factor using these 2 differing TBA frames (and the same glass
package) is: 0.29 (R-3.4) for the poorer performing frame, and 0.22 (R-4.5)
for the better frame.
I would say that putting either of those full frame u-factors in your energy
model will yield pretty different results.
I think its really important that we, as simulators and modelers, look at
full-frame performance because this is the system that will be installed in
the building. Center-of-Glass data can be useful comparing two different
glass packages, but at the end of the day, its a framed system that will be
installed and a framed system that should be analyzed. My 2¢.
Regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
email_sig
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential. If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Wednesday, July 14, 2010 1:10 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Window performance with frames
Does anyone know of a window manufacturer web site that has literature on
its windows including the frame? I am using Trace 700 for EA Credit 1 and
the reviewer asked for manufacturer data sheets for window performance
values (U-value, VLT and SHGC) including the frame.
Your help is appreciated,
Otto
____________________________________________________________________________
____________
Fanning/Howey Associates, Inc. intends to send this transmission (including
any attachments) only to the
designated individual or entity. If you received this message in error,
please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no
viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our authorization,
verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100716/dc11814f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5602 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100716/dc11814f/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100716/dc11814f/attachment-0001.jpeg>
More information about the Bldg-sim
mailing list