[Bldg-sim] Setpoint Temperature

Bishop, Bill wbishop at pathfinder-ea.com
Fri Jul 16 12:08:21 PDT 2010


Vinay,
 
If I understand you correctly, you want to know what the temperature difference is allowed to be between the actual space temperature and the setpoint temperature to define what an "unmet hour" is. In eQUEST, for example, this parameter is called the "throttling range", with a default value of 2°F for a proportional-type thermostat. Prior posts have suggested increasing the throttling range as a method of reducing unmet hours. I think this should be done as a last resort, but if you do it, you need to keep the same throttling range for both baseline and proposed for Appendix G. Unless the HVAC design is poor, the building has unusual load characteristics, or you are trying to model something outside of the capabilities of the simulation program, high unmet hours are often the result of "problems" in the model - mistakes in simulating the zones, systems, loads etc.
 
Regards,
Bill
 
William Bishop, PE, BEMP, LEED® AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Friday, July 16, 2010 2:23 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Setpoint Temperature
 
Hello All,

Appendix G guideline says 300 hours of setpoints not met is acceptable. Is there any Tolerance for heating/cooling setpoints not met? Or the temperatures have to be exact?

Thank you.

Regards,
Vinay
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100716/0ffbb28b/attachment.htm>


More information about the Bldg-sim mailing list