[Bldg-sim] LEED-NC v2.2 innovation in design credit for reduction in peak energy load

Robert Gengelbach rgengelbach at sustainablemech.com
Fri Jul 9 07:53:42 PDT 2010


Reduction in energy relates directly to  EAc1 and can be accounted for in that credit.  No ID credit would be available for reducing peak load.

 

cid:image003.png at 01C9AB43.F0BEE290

Robert Gengelbach, PE, LEED® AP

Sustainable Mechanical Design Associates, LLC

89 Monroe Center NW

Suite 302

Grand Rapids, MI 49503

P: (616) 776-9009

F: (616) 776-9010

C: (616) 570-2329

rgengelbach at sustainablemech.com

 

P Please print only if necessary

 

 

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of dlombard at earthlink.net
Sent: Friday, July 09, 2010 10:47 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED-NC v2.2 innovation in design credit for reduction in peak energy load

 


RE: innovation in design credit for reduction in peak energy load


 

Has anyone applied for and/ or gotten an innovation in design credit for reduction in peak energy load for any version of LEED? We're working on a project under LEED NC v2.2 and have significant reduction in lighting load during peak hours by using solatubes.

Please provide any contact info and details if you can.

I appreciate the assistance. It seems like the energy model can be manipulated to show the project savings during peak times and that would be enough information needed for a submittal to the GBCI.

THANKS for being LEEDers!!

Debra Lombard

dlombard at earthlink.net





-----Original Message----- 
From: Vinay Devanathan 
Sent: Jul 9, 2010 8:53 AM 
To: Demba Ndiaye 
Cc: "bldg-sim at lists.onebuilding.org" 
Subject: Re: [Bldg-sim] Exhaust Fans in Baseline 

Demba and Vikram,

Alright. Thanks for the clarification.

Regards,
Vinay

On Thu, Jul 8, 2010 at 5:35 PM, Demba Ndiaye <Demba.Ndiaye at setty.com> wrote:

Exhaust fan power is to be the same for both designs. You apportion the remaining baseline fan power allowance between supply and return/relief.

 

______________

Demba NDIAYE

 

From: Vinay Devanathan [mailto:vinay.devanathan at gmail.com] 
Sent: Thursday, July 08, 2010 5:29 PM
To: Sami, Vikram
Cc: Demba Ndiaye; bldg-sim at lists.onebuilding.org


Subject: Re: [Bldg-sim] Exhaust Fans in Baseline

 

Vikram,

Thanks for your reply. 

So, does it mean I will have to model the exhaust fan in the baseline model but in a fashion such that it consumes power proportionate to your proposed design (supply, return and exhaust) but falls within the Allowable Fan System bhp value of Appendix G. Am I right? 

Thank you.

Regards,
Vinay

On Thu, Jul 8, 2010 at 5:23 PM, Sami, Vikram <Vikram.Sami at perkinswill.com> wrote:

I'm pretty sure that your fan power allowance in 90.1 is for all fan energy (including exhaust). So for example if your baseline fan allowance is 20kW (hypothetical), you will need to apportion that allowance between supply and exhaust similar to your designed building. 

 

There was an extensive discussion about this around a year ago on this list (check the archives).

 

Vikram Sami, LEED AP

Sustainable Design Analyst

1382 Peachtree St. NE, Atlanta, GA 30309

t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com    <http://www.perkinswill.com/> www.perkinswill.com

Perkins+Will.  Ideas + buildings that honor the broader goals of society

 

 

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Thursday, July 08, 2010 5:15 PM
To: Demba Ndiaye
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Exhaust Fans in Baseline

 

Demba,

Thanks for your quick reply.

Regards,
Vinay

On Thu, Jul 8, 2010 at 5:13 PM, Demba Ndiaye <Demba.Ndiaye at setty.com> wrote:

Vinay, 

 

It is required to also model the exhaust fans in the Baseline. Use same cfm and fan powers as in the Proposed.

 

______________

Demba NDIAYE

 

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Thursday, July 08, 2010 5:09 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Exhaust Fans in Baseline

 

Hello All,

Do we have to model the exhaust fans also according to Appendix G for a Baseline model?
If yes, how should we design the cfm?

Thank you very much.

Regards,
Vinay

 


This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.

 





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100709/9eb8c746/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: application/octet-stream
Size: 12369 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100709/9eb8c746/attachment.obj>


More information about the Bldg-sim mailing list