[Bldg-sim] Exhaust Fans in Baseline
Sami, Vikram
Vikram.Sami at perkinswill.com
Thu Jul 8 14:23:44 PDT 2010
I'm pretty sure that your fan power allowance in 90.1 is for all fan energy (including exhaust). So for example if your baseline fan allowance is 20kW (hypothetical), you will need to apportion that allowance between supply and exhaust similar to your designed building.
There was an extensive discussion about this around a year ago on this list (check the archives).
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Thursday, July 08, 2010 5:15 PM
To: Demba Ndiaye
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Exhaust Fans in Baseline
Demba,
Thanks for your quick reply.
Regards,
Vinay
On Thu, Jul 8, 2010 at 5:13 PM, Demba Ndiaye <Demba.Ndiaye at setty.com<mailto:Demba.Ndiaye at setty.com>> wrote:
Vinay,
It is required to also model the exhaust fans in the Baseline. Use same cfm and fan powers as in the Proposed.
______________
Demba NDIAYE
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Vinay Devanathan
Sent: Thursday, July 08, 2010 5:09 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Exhaust Fans in Baseline
Hello All,
Do we have to model the exhaust fans also according to Appendix G for a Baseline model?
If yes, how should we design the cfm?
Thank you very much.
Regards,
Vinay
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100708/1ca5ae96/attachment.htm>
More information about the Bldg-sim
mailing list