Vinay,

It is required to also model the exhaust fans in the Baseline. Use same cfm and fan powers as in the Proposed.

______________
Demba NDIAYE

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Thursday, July 08, 2010 5:09 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Exhaust Fans in Baseline

Hello All,

Do we have to model the exhaust fans also according to Appendix G for a Baseline model?
If yes, how should we design the cfm?

Thank you very much.

Regards,
Vinay