[Bldg-sim] Check on FCU fan power calculations?
Jonathan Curtin
jcurtin at WylieAssociates.com
Tue Jan 12 08:34:14 PST 2010
James,
That's an error in ASHRAE 90.1-2004 that was later corrected in the
addenda and incorporated into the 2007 version. With the correction, the
fan power allowance drops by more than 50% (from what I recall) for
these small systems.
Regards,
Jonathan M. Curtin, EIT, LEED(r) AP
Mechanical Engineer
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Tuesday, January 12, 2010 10:21 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Check on FCU fan power calculations?
I was curious if anyone could confirm their experience with App G fan
power calculations for FCUs vs real life equipment values.
For AHUs, VAV boxes, etc, most average equipment consumes power nearly
identical to the fan power calculations of App G. Usually a little bit
better, but nothing major unless you start specifying ECM motors in VAV
boxes, fan walls for AHUs, etc.
But for FCUs: I've got a project with 100+, and most of them come out
to about 0.0008 KW / cfm per the calculations.
However, fairly standard FCU selections (from McQuay, not that it
matters), use about 0.0003 KW / cfm. That's almost a third of the
energy use, and when the entire building is FCU, it makes a huge
difference.
Can someone confirm their experience? I'm not complaining, but I just
want to make sure there isn't some addendum that changes the fan power
calcs for very low CFM HVAC systems.
Thanks!
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
------------------------------------------------------------------------------
Legal Disclaimer: The information contained in this communication is confidential and is covered by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any of the information contained within this communication. If you have received this communication in error, please contact the sender by telephone at (713) 781-2526 or by response via email and permanently delete the original email (including attachments) and any copies.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100112/aebb2678/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5651 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100112/aebb2678/attachment.jpeg>
More information about the Bldg-sim
mailing list