I would divide the 500 Watts by the entire 100 lineal feet of the wall the
fixture is on. I don't see what you would gain by just considering the lit
area of the wall but I can see where you might be penalized. Since it's just
an exterior load there aren't any interactive effects to worry about either.

Carol

On Thu, Feb 4, 2010 at 8:21 AM, Robby Oylear <robbyo at rushingco.com> wrote:

>  Can anyone with experience showing compliance with ASHRAE 90.1-2004
> section 9.4.5 enlighten me as how the baseline calculation should be done?
>
>
>
> The confusion I’m having is with the definition of an illuminated wall or
> surface length when applying the 5.0 W/linear foot allowance for building
> façades.  How is the lineal footage of an illuminated wall determined?
>
>
>
> For example, if a 100’ wide wall has one exterior lighting fixture on it at
> the center, is the entire wall considered to be illuminated and thus the
> baseline lighting power allowance is 500W?  Or is there some method of
> determining the actual portion of the wall that is illuminated?
>
>
>
> This came up on a LEED project where I had applied table 9.4.5 as
> conservatively as possible and only considered a portion of the wall to be
> illuminated at each fixture.
>
>
>
> Any help would be greatly appreciated.
>
>
>
> Robby Oylear, LEED® AP
>
> *Mechanical Engineer***
>
> direct: 206.788.4571
>
> cell: 206.354.2721
>
> *www.*rushingco.com <http://www.rushingco.com>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100204/63ef90f7/attachment.htm>


More information about the Bldg-sim mailing list