[Bldg-sim] Reset Boiler supply temp based on OA
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Feb 4 08:24:39 PST 2010
Allison,
Here are portions of the .inp file from an eQUEST model where I followed
the G3.1.3.4 requirement.
Regards,
Bill
"Hot-Water Supply Temp Reset" = DAY-SCHEDULE-PD
TYPE = RESET-TEMP
OUTSIDE-HI = 50
OUTSIDE-LO = 20
SUPPLY-HI = 180
SUPPLY-LO = 150
..
"Hot-Water Supply Temp Reset Week" = WEEK-SCHEDULE-PD
TYPE = RESET-TEMP
DAY-SCHEDULES = ( "Hot-Water Supply Temp Reset" )
..
"Hot-Water Supply Temp Reset Sch" = SCHEDULE-PD
TYPE = RESET-TEMP
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "Hot-Water Supply Temp Reset Week" )
..
"Hot Water Loop" = CIRCULATION-LOOP
TYPE = HW
LOOP-DESIGN-DT = 50
PIPE-HEAD = 21.6
LOOP-OPERATION = DEMAND
DESIGN-HEAT-T = 180
HEAT-SETPT-CTRL = OA-RESET
HEAT-RESET-SCH = "Hot-Water Supply Temp Reset Sch"
LOOP-PUMP = "HW Loop pump"
..
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Gaiko
Allison
Sent: Thursday, February 04, 2010 10:34 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Reset Boiler supply temp based on OA
Does anyone know how to model the boiler hot water supply temperature to
reset based on OA temp with Visual DOE? Or does anyone know how to
program it directly into the DOE-2 input? I am trying to meet the
ASHRAE 90.1-2004 section G3.1.3.4 requirement.
Allison Gaiko, PE, LEED AP
HVAC Engineer
A|H|A Consulting Engineers
Boston * Atlanta * Washington, DC
24 Hartwell Ave, Third Floor, Lexington MA, 02421
781- 372-3000(p) : 781-372-3100(f)
http://www.aha-engineers.com <http://www.aha-engineers.com/>
Allison_Gaiko at aha-engineers.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100204/f6290f30/attachment.htm>
More information about the Bldg-sim
mailing list