horizontal bands are no longer required. You can place the windows =
as-designed and run the baseline with the same windows (as long as you =
do not exceed 40% window-to-wall ratio).=20

-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com]On Behalf Of Andy =
McNamara
Sent: Thursday, February 15, 2007 9:39 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] eQUEST window baseline


Hello,

I am creating an energy model for a LEED project.  In "baselining" the =
building, one of the stipulations of ASHRAE 90.1 2004 is that the =
windows must be evenly distributed in horizontal bands on each facet of =
the facade.  My building has 17 facets due to a somewhat complicated =
design and I am wondering if anyone knows a relatively straightforward =
way to accomplish that distribution.  One of my problems is that in the =
Design Development Wizard, there are only 4 areas in which to enter =
percentages (N., E., S., W.) which doesn't seem to work on a building =
with so many facets.  On the other hand, it seems tedious to go into =
each window and adjust its percentage.  Is there a more elegant way to =
adjust window proportions globally?  I am thinking a parametric run =
might be the best solution.  Can anyone provide some insight on this?

Thank you!
Andrew McNamara



=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D

You received this e-mail because you are subscribed=20

to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe=20

from this mailing list send a blank message to=20

BLDG-SIM-UNSUBSCRIBE at GARD.COM



=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D

You received this e-mail because you are subscribed=20

to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe=20

from this mailing list send a blank message to=20

BLDG-SIM-UNSUBSCRIBE at GARD.COM



======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
------_=_NextPart_001_01C75148.3ADC1AD4
Content-Type: text/html;
	charset="iso-8859-1"
Content-Transfer-Encoding: quoted-printable

<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META HTTP-EQUIV=3D"Content-Type" CONTENT=3D"text/html; =
charset=3Diso-8859-1">
<TITLE>Message</TITLE>

<META content=3D"MSHTML 6.00.6000.16414" name=3DGENERATOR></HEAD>
<BODY>
<DIV><SPAN class=3D654541521-15022007><FONT face=3DArial color=3D#0000ff =
size=3D2>So, I=20
just got off the phone with the EA TAG member, and here are the basic =
items he=20
passed on to me:</FONT></SPAN></DIV>
<UL>
  <LI><SPAN class=3D654541521-15022007><FONT face=3DArial =
color=3D#0000ff size=3D2>The=20
  EA TAG recommended to the LEED steering group to allow all addenda, =
and there=20
  was no response stating the addenda should not be =
allowed</FONT></SPAN></LI>
  <LI><SPAN class=3D654541521-15022007><FONT face=3DArial =
color=3D#0000ff size=3D2>A=20
  recent CIR was submitted to allow all addenda for ALL ASHRAE =
standards, and=20
  the response allowing these addenda is not yet on the USGBC web page - =
and=20
  this could take weeks to months to actually be =
online</FONT></SPAN></LI></UL>
<DIV><SPAN class=3D654541521-15022007><FONT face=3DArial color=3D#0000ff =

size=3D2>Additionally, the EA TAG member mentioned that there are other =
issues=20
that have not been put on the website, or took longer (than it should =
have) to=20
appear on the web page. Examples were the approval of Title-24 and the =
Oregon=20
Energy Code being equivalent to ASHRAE 90.1-2004. </FONT></SPAN></DIV>
<DIV><SPAN class=3D654541521-15022007><FONT face=3DArial color=3D#0000ff =

size=3D2></FONT></SPAN>&nbsp;</DIV>
<BLOCKQUOTE dir=3Dltr style=3D"MARGIN-RIGHT: 0px">
  <DIV class=3DOutlookMessageHeader dir=3Dltr align=3Dleft><FONT =
face=3DTahoma=20
  size=3D2>-----Original Message-----<BR><B>From:</B> bldg-sim at gard.com=20
  [mailto:bldg-sim at gard.com]<B>On Behalf Of </B>Mike =
Tillou<BR><B>Sent:</B>=20
  Thursday, February 15, 2007 12:47 PM<BR><B>To:</B>=20
  bldg-sim at gard.com<BR><B>Subject:</B> [bldg-sim] eQUEST window=20
  baseline<BR><BR></DIV></FONT>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff=20
  size=3D2>Mitchell,</FONT></SPAN></DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff=20
  size=3D2></FONT></SPAN>&nbsp;</DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff size=3D2>Is=20
  that official or unofficial news from USGBC?&nbsp; As far as I =
understood LEED=20
  2.2 is using the version of Appendix G as written in ASHRAE 90.1-2004 =
without=20
  addenda.&nbsp; The change in Appendix G allowing you to use the actual =
window=20
  placement rather than equal banding on each facet was changed via =
ASHRAE=20
  addendum&nbsp;A in 2006&nbsp;which means it would NOT apply to LEED =
2.2=20
  projects.</FONT></SPAN></DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff=20
  size=3D2></FONT></SPAN>&nbsp;</DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff size=3D2>Here=20
  is the email response I got last month when I asked a member of the =
EA-TAG=20
  whether Addenda to 90.1-2004 applied to LEED 2.2.&nbsp;" =
</FONT></SPAN><SPAN=20
  class=3D099402820-15022007><SPAN=20
  style=3D"FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: =
Arial"><EM>Unfortunately it=20
  stops at 90.1-2004 and does not include addenda.&nbsp; The Reference =
Guide=20
  explicitly states &#8220;90.1-2004 (without =
amendments)&#8221;."</EM></SPAN></SPAN></DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff=20
  size=3D2></FONT></SPAN>&nbsp;</DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff size=3D2>Is=20
  there anyone from USGBC that can clarify this?</FONT></SPAN></DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff=20
  size=3D2></FONT></SPAN>&nbsp;</DIV>
  <DIV><SPAN class=3D099402820-15022007><FONT face=3DArial =
color=3D#0000ff=20
  size=3D2>Mike</FONT></SPAN></DIV><!-- Converted from text/rtf format =
-->
  <P><SPAN lang=3Den-us><FONT face=3D"Swis721 Blk BT" size=3D2>Michael =
Tillou,=20
  PE</FONT></SPAN> <BR><SPAN lang=3Den-us><FONT face=3D"Swis721 Blk BT" =
size=3D1>ETC=20
  Group - Energy Engineering for a Sustainable Future</FONT></SPAN> =
<BR><SPAN=20
  lang=3Den-us><FONT face=3D"Swis721 Blk BT" =
size=3D1>Ph:413-458-9870</FONT></SPAN>=20
  </P>
  <BLOCKQUOTE dir=3Dltr style=3D"MARGIN-RIGHT: 0px">
    <DIV></DIV>
    <DIV class=3DOutlookMessageHeader lang=3Den-us dir=3Dltr =
align=3Dleft><FONT=20
    face=3DTahoma size=3D2>-----Original Message-----<BR><B>From:</B>=20
    bldg-sim at gard.com [mailto:bldg-sim at gard.com] <B>On Behalf Of =
</B>Mitchell=20
    Dec<BR><B>Sent:</B> Thursday, February 15, 2007 12:54 =
PM<BR><B>To:</B>=20
    bldg-sim at gard.com<BR><B>Subject:</B> [bldg-sim] eQUEST window=20
    baseline<BR><BR></FONT></DIV>
    <DIV><SPAN class=3D466115217-15022007><FONT face=3DArial =
color=3D#0000ff=20
    size=3D2>From what I have been told by a member of the EA TAG is =
that the=20
    horizontal bands are no longer required. You can place the windows=20
    as-designed and run the baseline with the same windows (as long as =
you do=20
    not exceed 40% window-to-wall ratio). </FONT></SPAN></DIV>
    <BLOCKQUOTE>
      <DIV class=3DOutlookMessageHeader dir=3Dltr align=3Dleft><FONT =
face=3DTahoma=20
      size=3D2>-----Original Message-----<BR><B>From:</B> =
bldg-sim at gard.com=20
      [mailto:bldg-sim at gard.com]<B>On Behalf Of </B>Andy=20
      McNamara<BR><B>Sent:</B> Thursday, February 15, 2007 9:39 =
AM<BR><B>To:</B>=20
      bldg-sim at gard.com<BR><B>Subject:</B> [bldg-sim] eQUEST window=20
      baseline<BR><BR></FONT></DIV><SPAN=20
      class=3Dgmail_quote></SPAN>Hello,<BR><BR>I am creating an energy =
model for a=20
      LEED project.&nbsp; In "baselining" the building, one of the =
stipulations=20
      of ASHRAE 90.1 2004 is that the windows must be evenly distributed =
in=20
      horizontal bands on each facet of the facade.&nbsp; My building =
has 17=20
      facets due to a somewhat complicated design and I am wondering if =
anyone=20
      knows a relatively straightforward way to accomplish that=20
      distribution.&nbsp; One of my problems is that in the Design =
Development=20
      Wizard, there are only 4 areas in which to enter percentages (N., =
E., S.,=20
      W.) which doesn't seem to work on a building with so many =
facets.&nbsp; On=20
      the other hand, it seems tedious to go into each window and adjust =
its=20
      percentage.&nbsp; Is there a more elegant way to adjust window =
proportions=20
      globally?&nbsp; I am thinking a parametric run might be the best=20
      solution.&nbsp; Can anyone provide some insight on =
this?<BR><BR>Thank=20
      you!<BR>Andrew McNamara<BR =
clear=3Dall><BR></BLOCKQUOTE><PRE>=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D=3D
You received this e-mail because you are subscribed=20
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe=20
from this mailing list send a blank message to=20
BLDG-SIM-UNSUBSCRIBE at GARD.COM
</PRE></BLOCKQUOTE><PRE>
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D
You received this e-mail because you are subscribed=20
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe=20
from this mailing list send a blank message to=20
BLDG-SIM-UNSUBSCRIBE at GARD.COM
</PRE></BLOCKQUOTE><PRE>

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
</PRE></BODY></HTML>


------_=_NextPart_001_01C75148.3ADC1AD4--





More information about the Bldg-sim mailing list