[Bldg-sim] ASHRAE 90.1-2007 Fenestration Areas

Jason Glazer jglazer at gard.com
Wed Dec 22 14:38:28 PST 2010


The section of the standard states "Vertical fenestration 
areas for new buildings and additions shall equal that in 
the proposed design or 40% of gross abovegrade wall area, 
whichever is smaller, and shall be distributed on each face 
of the building in the same proportions in the proposed 
design." I've always assumed that you keep all the windows 
from the proposed design and just make them smaller. In your 
example since each window would be about 2/3 the proposed size.

Jason

On 12/22/2010 10:39 AM, Will Mak wrote:
> Hi all,
>
> I am working on a project that has a large amount of glass.
> ASHRAE 90.1-2007 states this about baseline modeling for glass:
>
> *The fenestration area in the baseline building shall be
> equal to the fenestration area in the proposed building or
> 40% of the exterior wall, whichever is less. If it is
> necessary to reduce window area in the baseline building,
> then corresponding increases are made in the opaque walls
> such that the gross exterior wall area is unchanged between
> the proposed building and the baseline building.*
>
> **
>
> *Fenestration area in the baseline building shall be
> distributed among the thermal blocks and around the building
> in a uniform manner. In each thermal block, the fenestration
> area shall be equal to the window wall ratio for the
> baseline building (the maximum of 40% or the proposed
> building WWR) multiplied times the exterior wall area for
> the thermal block. If the thermal block has more than one
> exterior wall, window area is placed proportionally on each. *
>
> **
>
> *The window area is positioned in continuous horizontal
> bands on each exterior wall, although the configuration of
> window area on each wall is not significant since neither
> daylighting or self shading from the building is modeled.
> See Figure G-D. *
>
> **
>
> *While the prescriptive envelope requirements provide an
> exception for street-level, street-side vertical
> fenestration (e.g., store display windows), the building
> performance rating method does not. Window area in the
> baseline building is always determined as described above.*
>
> **
>
> Based on the wordage above, I must develop the baseline
> model with either the same glass areas as the proposed
> building (essentially copying the proposed model and just
> updating U-values, etc.) or 40% of the exterior wall,
> whichever is smaller. Since I have roughly 60% of glazing, I
> will have to redistribute the glass into continuous
> horizontal bands on each exterior wall, similar to how
> ASHRAE 90.1-2004. However, as I began to look at the glass %
> of each exterior wall, I ran into a problem:
>
> *Wall*
>
> 	
>
> *Window SQ FT*
>
> 	
>
> *Wall SQ FT*
>
> 	
>
> *Total SQ FT*
>
> 	
>
> *Window %*
>
> North
>
> 	
>
> 10727.76
>
> 	
>
> 8485.95
>
> 	
>
> 19213.71
>
> 	
>
> 55.83%
>
> North-East
>
> 	
>
> 1812.26
>
> 	
>
> 2272.83
>
> 	
>
> 4085.09
>
> 	
>
> 44.36%
>
> East
>
> 	
>
> 2645.52
>
> 	
>
> 1846.83
>
> 	
>
> 4492.35
>
> 	
>
> 58.89%
>
> South-East
>
> 	
>
> 1683.46
>
> 	
>
> 1222.87
>
> 	
>
> 2906.33
>
> 	
>
> 57.92%
>
> South
>
> 	
>
> 12595.36
>
> 	
>
> 3958.92
>
> 	
>
> 16554.28
>
> 	
>
> 76.09%
>
> South-West
>
> 	
>
> 623.46
>
> 	
>
> 829.56
>
> 	
>
> 1453.02
>
> 	
>
> 42.91%
>
> West
>
> 	
>
> 3282.3
>
> 	
>
> 2924.38
>
> 	
>
> 6206.68
>
> 	
>
> 52.88%
>
> North
>
> 	
>
> 0
>
> 	
>
> 104.26
>
> 	
>
> 104.26
>
> 	
>
> 0.00%
>
> Total
>
> 	
>
> 33370.12
>
> 	
>
> 21645.6
>
> 	
>
> 55015.72
>
> 	
>
> 60.66%
>
> There is not enough exterior wall space to redistribute
> glazing to drop the percentages for each wall to 40%. Do I
> just reduce each wall to 40% glazing with continuous
> horizontal bands?
>
> Thanks!
>
> *William Mak, LEED Green Associate*
> Mechanical Design Engineer
>
> *EPSTEIN*
> Architecture
> Interiors
> Engineering
> Construction
>
> 600 West Fulton Street
> Chicago, Illinois 60661-1259
>
> D: (312) 429-8116
> F: (312) 559-1217
> E:wmak at epsteinglobal.com <mailto:wmak at epsteinglobal.com>
> W:www.epsteinglobal.com <http://www.epsteinglobal.com/>
>
> þEpstein is a firm believer in sustainability. We ask that
> you please consider the environment before printing this e-mail.
>
>
>