[Bldg-sim] heat gain of children?
Robert Gengelbach
rgengelbach at sustainablemech.com
Fri Dec 10 08:24:03 PST 2010
In the Ashrae fundamentals handbook there is a table of heat gains from
people at different activity levels in the non residential heating and
cooling loads chapter( Chapter 18 of the 2009 version). Children should be
calculated at 75% of the adult male heat gain value per that table, it has
been in the ASHRAE handbook for years.
cid:image003.png at 01C9AB43.F0BEE290
Robert Gengelbach, PE, LEEDR AP BD+C
Sustainable Mechanical Design Associates, LLC
89 Monroe Center NW
Suite 302
Grand Rapids, MI 49503
P: (616) 776-9009
F: (616) 776-9010
C: (616) 570-2329
www.sustainablemech.com
rgengelbach at sustainablemech.com
P Please print only if necessary
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Cramer
Silkworth
Sent: Friday, December 10, 2010 11:09 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] heat gain of children?
Hi All,
Has anyone out there every come across data for the heat gain of children
(for cooling load calcs)? I searched the ASHRAE handbooks but didnt find
anything, just the usual numbers for adults in the thermal comfort chapter.
My current thought is to use the adult numbers adjusted by mass, but if
there's real data that'd be great. Any hints would be appreciated.
-Cramer
--
Cramer Silkworth
212 219 2255 | silkworth at transsolar.com
Transsolar Inc. | 134 Spring Street Suite 601 | New York, NY 10012
Transsolar Climate Engineering
Technical consulting for energy efficiency and environmental quality in
buildings.
New York - Stuttgart - Munich
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101210/ae8ff188/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: application/octet-stream
Size: 12369 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101210/ae8ff188/attachment.obj>
More information about the Bldg-sim
mailing list