I'll take a crack at this. I am in agreement with you that CFMs comes
from/is used for the baseline model. If you look at the Option 2 on Table
6.5.3.1a you will notice the variable designated as A. Right below the same
Table, A is defined. It includes CFMd, which is information you would only
have from a proposed design building. So, I would say instead: CFMs,
modified using an Option 2 formula, which take into consideration CFMd when
appropriate, is what you use for your proposed design.
Hope this makes sense. As always, I am open for correction.
Carol
On Tue, Apr 13, 2010 at 12:52 PM, Caroline Fluhrer <cfluhrer at rmi.org> wrote:
> Hi there,
>
> For 90.1-2007 Table 6.5.3.1.1a & b, I am under the impression that "CFMs"
> comes from the baseline energy model ... should "CFMd" also come from your
> baseline model or should this be the actual proposed design flow through
> each device?
>
> Thank you,
> Caroline
>
> --
> Caroline E. Fluhrer
> Built Environment Team
> Rocky Mountain Institute
>
> 1820 Folsom St.
> Boulder, CO 80302 USA
> Main: 303.449.5226
> Direct: 303.567.8631
> Fax: 303.567.8626
> Email: cfluhrer at rmi.org
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100413/0f390da6/attachment.htm>
More information about the Bldg-sim
mailing list