[Bldg-sim] Easy Question

Dana Troy DTroy at glumac.com
Tue Apr 13 12:16:23 PDT 2010


All,

 

As per Addendum A to 90.1-2004, you do NOT need to distribute the baseline glazing uniformly in horizontal bands across the four orientations. ASHRAE 90.1-2007 is basically 90.1-2004 incorporating the changes made in Addendum A. All addenda can be found here: http://www.ashrae.org/technology/page/132

 

If you read Table G3.1.5, it only states that the glass must not exceed 40% and must be distributed by the same proportions as the proposed building. Therefore, if you have a building with 50% WWR, you just have to reduce each window by 20%. This will still ensure that you have the same proportions (e.g. 20% of all of the glass on the north, 30% of all of the glass on the south, 40% of all of the glass on the east, and 10% of all of the glass on the west).

 

If your baseline WWR is less than 40%, then leave the window proportions, shapes, and sizes the same in the baseline and the proposed design.

 

This has all been well documented on the archives as well: http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2007-April/004077.html

 

Regards,


Dana Troy
Energy Analyst
LEED® Accredited Professional

  <http://www.glumac.com/> 

________________________________

320 SW Washington, Suite 200
Portland, OR 97204-2640
T.  503.227.5280  F. 503.274.7674

Thinking. Inside the building.
www.glumac.com <http://www.glumac.com/>  
 

 

From: Carol Gardner [mailto:cmg750 at gmail.com] 
Sent: Tuesday, April 13, 2010 11:58 AM
To: Rimes, Christie
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Easy Question

 

Perhaps I'm missing something, but didn't he ask us how to calculate the window to wall ratio? If I'm not missing something, we need to know specifically, is the wall number wall only or wall + glass. This level of information is shown on the LV-D report in eQUEST, if he's using eQUEST. That's why I said, "it depends".

Carol

On Tue, Apr 13, 2010 at 11:45 AM, Rimes, Christie <Christie.Rimes at wspfk.com> wrote:

For the 90.1-2004 I have always taken it as Luke explained, evenly distributed the WWR of the entire building.

However for 90.1-2007 I have interpreted the description to mean that the windows stay in the same location as the proposed building?

 

 

Error! Filename not specified.

 

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Tuesday, April 13, 2010 11:38 AM
To: JohannesHopf; bldg-sim at lists.onebuilding.org; LukeWilson


Subject: Re: [Bldg-sim] Easy Question

 

Interesting point. I've never noticed this before, but this is different from 2004. 

 

2004 stated :

 

Vertical fenestration areas for new buildings and additions shall equal that in the proposed design or 40% of gross abovegrade wall area, whichever is smaller, and shall be distributed uniformly in horizontal bands across the four orientations.

 

It looks like they have changed it (shall be distributed on each face of the building in the same proportions in the proposed design) to be more representative of the actualy building. I think 2007 is asking you to distibute it by orientation (if you have 40% on the west, 25% south, 20%north and 25% east in your design, you will have 40% on the west, 25% south, 20%north and 25% east in your baseline). This makes sense because otherwise we were doing the striping as well as the 4 rotations which was a little redndant. 

 

(Not so easy question after all, but a good one). 

 


--- On Tue, 4/13/10, Wilson, Luke <LWilson at integral-group.net> wrote:

	
	From: Wilson, Luke <LWilson at integral-group.net>
	Subject: Re: [Bldg-sim] Easy Question
	To: "Hopf, Johannes" <johannes.hopf at dreso.com>, "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
	Date: Tuesday, April 13, 2010, 10:05 AM

	ASHRAE 90.1-2007 Table G3.1 reads:
	"Vertical fenestration areas for new buildings and additions shall equal that in the proposed design or 40% of gross above-grade wall area, whichever is smaller, and shall be distributed on each face of the building in the same proportions in the proposed design."
	
	I wasn't aware that this requirement had changed in the 2007 version (thanks Cam!).
	
	Luke
	
	-----Original Message-----
	From: bldg-sim-bounces at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim-bounces@lists.onebuilding.org>  [mailto:bldg-sim-bounces at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim-bounces@lists.onebuilding.org> ] On Behalf Of Hopf, Johannes
	Sent: Tuesday, April 13, 2010 12:55 PM
	To: bldg-sim at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim@lists.onebuilding.org> 
	Subject: Re: [Bldg-sim] Easy Question
	
	I can't find this section in Table 1.3.? I just find the 40% limitation for
	the baseline building. Can you post an excerpt?
	
	
	Best regards
	
	 
	Johannes 
	
	-----Ursprüngliche Nachricht-----
	Von: bldg-sim-bounces at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim-bounces@lists.onebuilding.org> 
	[mailto:bldg-sim-bounces at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim-bounces@lists.onebuilding.org> ] Im Auftrag von Wilson, Luke
	Gesendet: Dienstag, 13. April 2010 17:18
	An: Eurek, John S NWO; bldg-sim at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim@lists.onebuilding.org> 
	Betreff: Re: [Bldg-sim] Easy Question
	
	John,
	
	I'm assuming you are using ASHRAE 90.1-2007 Appendix G for your Baseline?
	If so, the way I read it from Table G3.1 is that you should evenly distribute
	the WWR of the entire building, not for each floor. Therefore I would use
	11.4% for each floor.
	
	Luke
	
	-----Original Message-----
	From: bldg-sim-bounces at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim-bounces@lists.onebuilding.org> 
	[mailto:bldg-sim-bounces at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim-bounces@lists.onebuilding.org> ] On Behalf Of Eurek, John S
	NWO
	Sent: Tuesday, April 13, 2010 10:22 AM
	To: bldg-sim at lists.onebuilding.org <http://us.mc656.mail.yahoo.com/mc/compose?to=bldg-sim@lists.onebuilding.org> 
	Subject: [Bldg-sim] Easy Question
	
	I have a two story building.  For the baseline I am evenly distributing the
	fenestration.
	
	The first floor window area is 462.2 ft^2
	The second floor window area is 647.1 ft^2
	
	The first floor wall area is 4858 ft^2
	The second floor wall area is 4858 ft^2
	
	In the base line model do I use:
	
	First floor 9.5%
	Second floor 13.3%
	
	OR
	
	First floor 11.4%
	Second floor 11.4%
	_______________________________________________
	Bldg-sim mailing list
	http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
	To unsubscribe from this mailing list send  a blank message to
	BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG> 
	
	
	This email and any files transmitted with it are confidential and intended
	solely for the addressee.  If you are not the named addressee you should not
	disseminate, distribute, copy, or alter this email.
	_______________________________________________
	Bldg-sim mailing list
	http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
	To unsubscribe from this mailing list send  a blank message to
	BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG> 
	
	
	_______________________________________________
	Bldg-sim mailing list
	http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
	To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG> 
	
	_______________________________________________
	Bldg-sim mailing list
	http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
	To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <http://us.mc656.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG> 

 


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100413/056e6e08/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 50453 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100413/056e6e08/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1425 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100413/056e6e08/attachment-0001.gif>


More information about the Bldg-sim mailing list