[Bldg-sim] Multiple Buildings
David S Eldridge
DSE at grummanbutkus.com
Tue Oct 27 16:54:10 PDT 2009
A few things to consider:
Are the buildings part of the same project or building permit? - if separate then 90.1 would apply to them individually. This is regardless of grouping them into one LEED project for instance.
The definition of "building" in 90.1-2004 is "a structure wholly or partially enclosed within exterior walls..." - so even if combined into one building permit, these three might be treated as separate buildings for system selection purposes, especially if the predominant usage for the three is different based on Exception (a) to G3.1.1 (assuming you are using the Performance Rating Method and not ECB since you are discussing the building sizes).
Hope this helps, good luck!
David
____________________________________________________________________________________________________________________
David Eldridge, PE
LEED(r) AP, HBDP
Grumman/Butkus Associates | 820 Davis Street, STE 300 | Evanston, IL 60201 | Ph: (847) 328-3555, ext 224 | Fax: (847) 328-4550
http://www.grummanbutkus.com
Energy Consultants and Design Engineers
____________________________________________________________________________________________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Scott Haag
Sent: Tuesday, October 27, 2009 5:05 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Multiple Buildings
All;
I have a project with multiple buildings on one site to model. When determining the correct baseline HVAC system, should I do this on an individual building basis, or use the same system for all buildings and base it on the summation of all of the buildings' areas?
The first building is 3-stories and 190,000 square feet, the second building is 1 story and 44,000 square feet, and the third building is 1 story and 8,000 square feet.
I have tried searching old posts with no success. Thanks for your help.
Scott
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091027/5099f068/attachment.htm>
More information about the Bldg-sim
mailing list