[Bldg-sim] Underfloor air - more questions
Steve Mignogna
smignogna at gmail.com
Thu Oct 22 14:08:10 PDT 2009
Vikram,
Also, do not forget that since you are now able to supply the air at a
higher temperature you can set your outside economizer at a higher
temperature as well. Alot of the savings from displacement type air
distribution systems come from the increased outside air economizer use.
Good luck.
--
Steve Mignogna
Atelier Ten
On Thu, Oct 15, 2009 at 7:14 PM, Chris Jones <cj at cr-jay.ca> wrote:
> Check this document:
> http://www.bkbiz.net/Website/BMEA/Underfloor%20Air%20Distribution.pdf
>
>
>
> We have this historic building that we are renovating and are considering
> underfloor air distribution. The space is a high bay space (around 50 feet
> tall) that will be occupied by students with computers. The design currently
> has an access floor 6” above the existing floor. We are thinking of raising
> it a little more and running the supply air through underfloor ducts (we
> can’t do a plenum because of the condition of the existing floor).
>
> As far as I can tell the energy benefits of the underfloor air system are:
>
> 1. Higher supply air temperature (68F)
> 2. Lower static pressure
> 3. Stratification (lights, equipment and people heat stratifies above
> the return air grills.
>
> The alternate is a supply duct that throws air across the space (60 feet
> wide) from a height of 20 feet.
>
> So my questions are:
>
> 1. If the UFAD goes through ducts (as opposed to a plenum) is the
> reduced static pressure realistic? How much would you expect to see it
> reduce by?
> 2. How much stratification can you expect here? I assume there is a
> radiant portion from these things in addition to the convective portion.
> Would a 50% reduction in the sensible loads be realistic? I know the normal
> procedure would be to assign the rest of the loads to the return plenum, but
> it this case the return will be ducted at 8’, while the warm air will be
> allowed to plume up to 50. Does that change things?
> 3. I assume I should model the upper part of the zone as a plenum. In
> which case – does the upper plenum start at 20’ for the alternate system
> (spiral duct at 20’), and at 8’ for the UFAD?
>
> All responses are appreciated
>
> Thanks
>
> *Vikram Sami,* LEED AP
> Direct Phone 404-253-1466 | Direct Fax 404-253-1366
> *LORD, AECK & SARGENT ARCHITECTURE
> *1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
> Responsive Design · Technological Expertise · Exceptional Service
> Please visit our new website | www.lordaecksargent.com
> P Think GREEN before you print.
>
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4512 (20091015) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 4512 (20091015) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
> Chris Jones
> 14 Oneida Avenue
> Toronto, ON M5J 2E3.
> Tel. 416-203-7465
> Fax. 416-946-1005
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091022/e28636c1/attachment.htm>
More information about the Bldg-sim
mailing list