[Bldg-sim] Glazing heat transfer
D. Charlie Curcija
curcija at designbuildersoftware.com
Tue Oct 13 15:08:29 PDT 2009
SHGC is calculated as Tsol + inward flowing fraction, which takes into
account inside temperature and absorbed heat in the glass, so convective
and FIR radiative gain from solar radiation is incorporated into the
SHGC. U-factor that contributes to heat transfer without solar
radiation is always positive and so delta T where indoor temperature is
lower than outdoor temperature would result in a net heat gain to the
space, not the heat loss that you are seeing. However, note several
other factors. Temperature changes over the 24 hours each day, radiant
temperature of the sky is normally much lower than the air temperature,
so when you have very small average indoor to outdoor delta T, these
things can switch direction of heat flow. I guess, you would need to
look at each hour and look at the specifics.
Charlie Curcija
DesignBuilder Software USA
-------- Original Message --------
Subject: Re: [Bldg-sim] Glazing heat transfer
From: Raoni Venâncio dos Santos Lima <raoniv at ig.com.br>
To: rgaray at labein.es, bldg-sim at lists.onebuilding.org
Date: 10/13/2009 9:47 AM
> This was my hypothesis, but none of my DesignBuilder students bought
> that. Indeed, the glass surfaces temperatures (internal and external)
> were higher than the outside temperature. On the other hand, the
> internal temperature was lower than outside temperature. Apparently
> the glass tends to lose heat from its external surface to the outside
> air (probably maximized by convection) and to gain some heat due to
> conduction (from outside air to internal air). In this case, my glass
> is losing more heat.
>
> I appreciate your reply,
> Best regards,
>
> Raoni.
>
>
>
>
> 2009/10/13 <rgaray at labein.es <mailto:rgaray at labein.es>>
>
>
> Dear Raoni,
>
> I´m not completely of the calculation method used by Energy Plus,
> There are several reasons an outward heat flux in the outer
> surface of a glazing system:
>
> The usual one is when the outside temperature is colder than the
> one inside. As you tell in your post, this is not the case in your
> simulations.
>
> There is a second reason that only happens when both internal and
> external temperatures are nearly the same (even beein the internal
> one a little bit lower than the external one): The glazing is
> heated by the incoming solar radiation and its temperature rises
> over the external temperature. This creates an outward heat flux.
> For a clear glass, the usual absorptance is very low (1-4%) so
> this phenomenom is usually very rare.
>
> I don´t know is this info will solve your problem.
>
> Kind regards,
>
> --------------------------------------------------------------------------
> Roberto Garay Martinez
> Labein-Tecnalia
> Unidad de Construcción y Desarrollo del Territorio
> c/Geldo. Parque Tecnológico de Bizkaia
> Edificio 700
> 48160 Derio (Bizkaia)
> Tel.: 34 94 607 33 00
> Fax: 34 94 607 33 49
> www.labein.es <http://www.labein.es>
> --------------------------------------------------------------------------
> Bilbao, 17-19 de Mayo, 2010
> Open and Sustainable Building
> Edificación Adaptable y Sostenible
> www.OpenBuilding-2010.org <http://www.OpenBuilding-2010.org>
> --------------------------------------------------------------------------
>
>
>
>
> ----- Mensaje de Raoni Venâncio dos Santos Lima <raoniv at ig.com.br
> <mailto:raoniv at ig.com.br>> en Fri, 9 Oct 2009 16:46:37 -0300 -----
> *Para:*
> bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> *Asunto:*
> [Bldg-sim] Glazing heat transfer
>
>
> Dear colleagues,
>
> I've noticed a slight heat loss through glazed surfaces during the
> whole
> year. I'm usind DesignBuilder and the situation is the following:
> 1) climate: Brasilia (Brazil). Average temperatures around 22°C,
> but during
> occupied periods (daytimes) the temperatures are higher (around
> 26°C). Solar
> radiation is considerable.
> 2) Conditioned zone with 24°C set point temperature
> 3) Using a single pane glass 3mm (SHGF around 89%) form the EnergyPlus
> dataset.
>
> I wonder why the zone is losing heat through glazing even when
> internal
> temperatures are lower than external (conditioned zone). Heat
> gains due to
> solar radiation are ok, but I'm not sure the glazing results are
> fine. The
> interesting thing is that the zone never gains heat from the
> glazing (except
> due to solar radiation).
>
> Is this a common thing? Any thoughts?
>
> Thanks in advance,
> Raoni
>
>
>
> ---------------------------------------------------------------------------------------------------------------------------------------------------------------------
>
> Imprime sólo lo imprescindible, recuerda tu compromiso con el
> MEDIO AMBIENTE // Behar beharrezkoa baino ez imprimatu, gogoratu
> zure INGURUGIROArekiko konpromezua // Before printing think about
> the ENVIRONMENT
>
> ---------------------------------------------------------------------------------------------------------------------------------------------------------------------
>
> Este mensaje se dirige exclusivamente a su destinatario y puede
> contener información privilegiada o confidencial. Si no es vd. el
> destinatario indicado,
> queda notificado de que la utilización, divulgación y/o copia sin
> autorización está prohibida en virtud de la legislación vigente.
> Si ha recibido este mensaje por error, le rogamos que nos lo
> comunique inmediatamente por esta misma vía y proceda a su
> destrucción.
>
> Mezu honek eta erantsita dituen agiriek (baldin baditu) isilpeko
> informazioa izan dezakete. Hori dela eta, hutsegite baten ondorioz
> jasotzen duenak
> jakin beza bertan dagoen informazioa ezkutukoa dela eta legeak
> galarazi egiten duela berori baimenik gabe erabiltzea.
>
> This message is intended exclusively for its addressee and may
> contain information that is confidential and protected by
> professional privilege.
> If you are not the intended recipient you are hereby notified that
> any dissemination, copy or disclosure of this communication is
> strictly prohibited by law.
> If this message has been received in error, please immediately
> notify us via e-mail and delete it.
> ---------------------------------------------------------------------------------------------------------------------------------------------------------------------
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091013/37feb840/attachment.htm>
More information about the Bldg-sim
mailing list