[Bldg-sim] ASHRAE 62.1 unoccupied space minimum outdoorairsupply
Brahme, Rohini UTRC
BrahmeR at utrc.utc.com
Thu Nov 12 10:11:41 PST 2009
Thanks Nick. The reason I had the question was because I think OA/sqft
technically should not be dependent on occupancy. If that was the case,
it would suffice to just increase the OA/sqft and have only one number
to take care of. What I am not sure of is whether OA/sqft is used only
during the typical occupied hours irrespective of whether it is actually
occupied or not or is it used throughtout the day/weekend/vacation etc.
What do the hvac designers specify for the control of OA?
-rohini
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Thursday, November 12, 2009 12:22 PM
To: Brahme, Rohini UTRC; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] ASHRAE 62.1 unoccupied space minimum
outdoorairsupply
I havn't read the standard in detail, but isn't there a requirement of
some OA/sqft in addition to OA/person.
You are correct. Refer to the equation of Section 6.2.2.1 as I
referenced below.
Let's assume that an office is assumed normally occupied from 8 am to 6
pm - Then during unoccupied hours (6.01 pm to 7.59 am) can the OA be
zero or should it be OA per sqft?
It sounds like you're asking the same question I just answered, so I may
not be understanding completely... By Section 5.4 I do not believe an
unoccupied space is required to have any OA supplied. The equation in
6.2.2.1 does include a component "per square foot," but that equation is
for determining the design minimum OA rate.
More tricky, let's say we have a occupancy sensor and know that the
office is unoccupied from 12.00 pm to 3 pm (during the regular office
times). What is the OA at this time - 0 or OA/sqft?
Applying the same logic and the same section, 5.4, if there are controls
that automatically determine a space is occupied and turn the associated
system on to provide the required OA, then there's no reason those
systems aren't allowed to turn off while unoccupied. Short answer for
your example: 0.
I'll point out, I'm merely an E.I.T. (with my head in the books) sharing
my interpretations, so it may be worth holding out for a second opinion
=).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Brahme,
Rohini UTRC
Sent: Thursday, November 12, 2009 11:14 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 62.1 unoccupied space minimum
outdoorairsupply
Since we are on this topic, I had a question on definition of occupancy.
I havn't read the standard in detail, but isn't there a requirement of
some OA/sqft in addition to OA/person.
Let's assume that an office is assumed normally occupied from 8 am to 6
pm - Then during unoccupied hours (6.01 pm to 7.59 am) can the OA be
zero or should it be OA per sqft?
More tricky, let's say we have a occupancy sensor and know that the
office is unoccupied from 12.00 pm to 3 pm (during the regular office
times). What is the OA at this time - 0 or OA/sqft?
Thanks
-rohini
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Thursday, November 12, 2009 11:36 AM
To: Guin, Michael; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 62.1 unoccupied space minimum
outdoorairsupply
No.
Refer to Section 5.4:
"Mechanical ventilation systems shall include controls, manual or
automatic, that enable the fan system to operate whenever the spaces
served are occupied. The system shall be designed to maintain the
minimum outdoor airflow as required by Section 6 under any load
condition."
In summary, you must provided the minimum ventilation rate as prescribed
in Chapter 6 only when (A) the space is occupied and (B) there's a
thermal load condition (or manual control - see Section 5.4) triggering
the operation of the ventilation system.
Your original question is confusing to at least a few of us because of
stating an office ceases to be a "zone" at night... It's a terminology
thing, but 62.1 and other standards will become more digestible to you
when you recognize that's not the case. The clarification we're making
here is that where a zone occupancy (i.e. "office") is decided and a
constant over time, something like "occupancy rate" can be variable.
I'd like to also point out, based on your first inquiry, that the
equation at 6.2.2.1 uses maximum zone occupancy to establish the minimum
design OA rate, not the hourly occupancy rate (which may be zero).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Guin,
Michael
Sent: Thursday, November 12, 2009 8:44 AM
To: Shawn.Lee at fluor.com
Cc: bldg-sim-bounces at lists.onebuilding.org;
bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 62.1 unoccupied space minimum outdoor
airsupply
is there any requirement to provide minimum outdoor fresh air wihin the
office space when it is unoccupied according to ASHRAE 62.1
Do you think it it clear enough?
Regards
Michael
________________________________
From: Shawn.Lee at fluor.com [mailto:Shawn.Lee at fluor.com]
Sent: 12 November 2009 13:58
To: Guin, Michael
Cc: bldg-sim at lists.onebuilding.org;
bldg-sim-bounces at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 62.1 unoccupied space minimum outdoor air
supply
Michael,
Technically answering your question may not help you much. You need to
make the question clearer and more meaningful. Tell people what you are
trying to do, what is in your mind, and what you are trying to
accomplish. Then this group may help you more on the target.
Thanks.
Shawn Lee, PhD, PE
"Guin, Michael" <Michael.Guin at WSPGroup.com>
Sent by: bldg-sim-bounces at lists.onebuilding.org
11/12/2009 06:09 AM
To
<bldg-sim at lists.onebuilding.org>
cc
Subject
[Bldg-sim] ASHRAE 62.1 unoccupied space minimum outdoor air supply
Dear all,
ASHARE 62.1 2007 deifned zone as an occupied space. Table 6-1 provides
the calculation for different spaces based on occupancy and floor area
of the occupied space.
If we consider an unoccupied office space at night (i.e. not strictly a
"zone anymore" ); is there any requirement to provide minimum fresh air
wihin the office space.
Thanks in advance for your help
Michael
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain
proprietary, business-confidential and/or privileged material.
If you are not the intended recipient of this message you are
hereby notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon
this message is prohibited. If you received this in error, please
contact the sender and delete the material from any computer.
Any views expressed in this message are those of the individual
sender and may not necessarily reflect the views of the company.
------------------------------------------------------------
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091112/7f8bcb35/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091112/7f8bcb35/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list