[Bldg-sim] Ground Source Water-to-Water HP in eQuest

Nick Caton ncaton at smithboucher.com
Tue Nov 3 07:37:11 PST 2009


That's pretty much what I've done for a few projects.

 

1.       Calc your loads incident on the loop, either using eQuest or
another program

2.       Use those loads to determine the annual thermal behavior of the
ground loop using a program like the free GS2000 or a similar
ground-loop design tool.

3.       Use the thermal behavior output of your ground-loop software of
choice to create a custom temperature schedule.  If you want a more
detailed explanation of the step-by-step process within eQuest, search
for my name in the eQuest/Bldgsim archives.

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jackson,
Alan
Sent: Tuesday, November 03, 2009 9:20 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Ground Source Water-to-Water HP in eQuest

 

I believe the methodology that has been implemented with success is to
use the WTW HPs with the lake well, but to use a schedule for well water
temperatures either taken from a separate run with WTA and closed loop,
or to take the temperatures from another yearly sim in either GLHE-PRO
or GS2000.

 

 

Alan Jackson, LEED AP
KlingStubbins

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Garcia,
Robert
Sent: Tuesday, November 03, 2009 10:04 AM
To: 'bldg-sim at lists.onebuilding.org'
Subject: [Bldg-sim] Ground Source Water-to-Water HP in eQuest

 

This topic appears to be a gray area within eQUEST.  Has anyone been
able to successfully model a Ground Source Water-to-Water HP connected
to a closed loop Geothermal Well Field?

 

The WWHP is to serve a radiant floor.  In addition to the WWHP, the
design also has multiple Water-to-Air Heat Pumps connected to the same
well field.  Issues rise when trying to figure out how to model the
effect of the WWHP on the Well Loop.  

 

In the past I have used the Loop-to-Loop Chiller to model a WWHP, but
the chiller requires a connection to a Lake-Well type loop.  

 

Thanks in advance.

 

Robert Garcia |AKF|

 

 

 


This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended
recipient of this e-mail, do not duplicate or redistribute it by any
means. Please delete it and any attachments and notify the sender that
you have received it in error. Unintended recipients are prohibited from
taking action on the basis of information in this e-mail. E-mail
messages may contain computer viruses or other defects, may not be
accurately replicated on other systems, or may be intercepted, deleted
or interfered without the knowledge of the sender or the intended
recipient. If you are not comfortable with the risks associated with
e-mail messages, you may decide not to use e-mail to communicate with
AKF. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091103/b60e96d1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091103/b60e96d1/attachment-0002.jpeg>


More information about the Bldg-sim mailing list