[Bldg-sim] Why should roofs have high emissivity?
David Bryan
dbryan at amerindian.com
Sun Nov 29 18:34:25 PST 2009
Remember that emissivity and absorptivity are generally equal and often
vary with wavelength. And for opaque materials, emissivity generally
equals (1- reflectivity) at a given wavelength.
So it would be possible to have a spectrally selective roof which
reflected the sun's visible and short wave infrared energy well (high
reflectance, low emittance) but also radiated energy well at the longer
infrared wavelengths emitted at its temperature rather than the sun's
(low reflectance, high emittance). This would be the ideal cool roof
material.
This roofing material probably exists.
Dave Bryan
Third Level Design
Brad Painting wrote:
> It seems to me that a roof that emits more radiation will have a
> greater warming effect on the building. Some houses in warm climates
> have radiant barriers because the aluminum has a /low/ emissivity,
> thus blocking the infrared radiation. But both LEED and Energy Star
> suggest high emissivity for warm climates. Does this make sense?
>
> From LEED NC Reference Guide v. 2.2:
>
> "To maximize energy savings and minimize heat island effects,
> materials must exhibit a high reflectivity and a high emissivity over
> the life of the product."
>
> >From Energy Star website:
>
> "In warm and sunny climates highly emissive roof products can help
> reduce the cooling load on the building by releasing the remaining
> heat absorbed from the sun."
>
> Thanks,
>
> Brad
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091129/4e89e0da/attachment.htm>
More information about the Bldg-sim
mailing list