[Bldg-sim] Baseline Modeling for LEED
Marzia Sedino
marzia.sedino at som.com
Thu Nov 19 13:38:25 PST 2009
Steven, I would apply the same ventilation rates to both baseline and proposed
check appendix G.3.1.2.5 - it says minimum OA rates have to be consistent in the two models.
marzia
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Steven Rutter
Sent: Thursday, November 19, 2009 4:25 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Baseline Modeling for LEED
All,
There is a credit in LEED (EQc2.0) that involves increasing the required ventilation rate by 30%. In trying to achieve this credit, the amount of energy would have to increase to condition that additional 30% OSA. Does anyone know if you are supposed to increase the baseline energy model's ventilation rate so it has the same ventilation rate as the proposed building? Thank you in advance for your help.