[Bldg-sim] Mud phuska properties

Chip Barnaby cbarnaby at wrightsoft.com
Mon Nov 9 06:01:50 PST 2009


All,
Please check this info.  The quoted density is less than 
fiberglass.  Mud phuska is a mix of clay and wood shavings (right?), 
so the density should be > 500 kg/m3.  Solid wood is around 500, soil 
is 1500 - 1900.  The conductivity and specific heat are more plausible.
Chip Barnaby

At 06:50 AM 11/9/2009, Meenakshi Sahu wrote:
>Dear Sanyogita,
>
>Please note down the following properties of mud phuska.
>
>Density = 1.731 kg/m^3
>Thermal conductivity = 0.750 W/mK
>Specific heat capacity = 0.88 kJ/kg-K
>[Reference: SP 41, Handbook on functional requirements of building 
>(Other than industrial buildings), Part 1-4, Bureau of Indian Standard (1988)]
>
>
>  Regards,
>Meenakshi.
>
>--- On Mon, 9/11/09, sanyogita manu <sanyogitamanu at yahoo.com> wrote:
>
>From: sanyogita manu <sanyogitamanu at yahoo.com>
>Subject: [Bldg-sim] Mud phuska properties
>To: bldg-sim at lists.onebuilding.org
>Date: Monday, 9 November, 2009, 12:29 PM
>
>Hi
>
>I know its a long shot but does anyone know what are the thermal and 
>surface properties of Mud phuska? It is a typical Indian roof 
>insulation. I would be very grateful if I could get a reference to a source.
>
>Thanks and regards,
>
>
>Sanyogita
>
>
>-----Inline Attachment Follows-----
>
>_______________________________________________
>Bldg-sim mailing list
><http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>Now, send attachments up to 25MB with Yahoo! India Mail. 
><http://in.rd.yahoo.com/tagline_galaxy_2/*http://in.overview.mail.yahoo.com/photos>Learn 
>how.
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

---------------------------------------------------------
Chip Barnaby                   cbarnaby at wrightsoft.com
Vice President of Research
Wrightsoft Corp.               781-862-8719 x118 voice
131 Hartwell Ave               781-861-2058 fax
Lexington, MA 02421         www.wrightsoft.com
--------------------------------------------------------- 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091109/e7bdcee5/attachment.htm>


More information about the Bldg-sim mailing list