[Bldg-sim] effect of films on SHGC of glazing
D. Charlie Curcija
curcija at designbuildersoftware.com
Fri May 22 13:32:35 PDT 2009
OPTICS program from LBNL will calculate optical properties of substrate
glazing with applied film. After the model is completed in OPTICS, you
can import such layer in WINDOW program and calculate SHGC of
multi-layer glazing, where one of the layers is glass with applied film,
imported from OPTICS.
Charlie Curcija
DesignBuilder Software
> Dear all,
>
> Is there an accepted way of calculating the effect of a film on the
> SHGC of glazing? Does LBL's Window or any other tool help with such a
> calculation?
>
> Thanks,
> Ramana.
>
>
> ------------------------------------------------------------------------
>