[Bldg-sim] [Equest-users] Heat Recovery Chiller
Steve Mignogna
smignogna at gmail.com
Thu Mar 12 09:24:37 PDT 2009
Tony-
When you define a chiller in eQuest, along with assigning the appropriate
CHW (and possibly CW and HW) there is also a loop assignment for "HtRec".
This takes either a HW, WLHP, or DHW Loop to which the chiller will attempt
to provide recovered heat to. There are some variables you will need to
fill in depending on how much heat you want to recover, etc...
If that doesn't answer your question, please let me know.
Regards,
--
Steve Mignogna
Atelier Ten
On Mon, Mar 9, 2009 at 4:55 PM, Tony Kriel <tkriel at sustaineng.com> wrote:
> I know this has been asked once or twice before, but I haven’t had too
> much luck finding an appropriate archived response.
>
>
>
> Has anyone successfully modeled a heat recovery chiller in Equest that
> would reject heat to a domestic hot water loop and would like to share a
> step by step process for simulating such a system?
>
>
>
> Thanks,
>
>
>
> Tony Kriel, LEED AP
>
> Mechanical Engineer
>
> tkriel at sustaineng.com
>
> (608) 231-9664 ext. 16
>
>
>
> Sustainable Engineering Group, LLC.
>
> 431 Charmany Drive, Suite 102
>
> Madison, WI 53719
>
> www.sustaineng.com
>
>
>
> <tkriel at sustaineng.com>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090312/2d4242d3/attachment-0001.htm>
More information about the Bldg-sim
mailing list