[Bldg-sim] Window overhangs at 30 degrees
Charudatta Joshi (CJ)
csjoshi at asu.edu
Tue Mar 10 06:34:50 PDT 2009
Teck,
1. You will need to be in the 'Detailed Data Edit Mode' to be able to
accomplish this.
2. Once there, check the properties of a window and get to the
'Fins-Overhang' tab.
3. Change the angle (OAng) to 60 degree - that will actually give you the
30 deg downward tilt you want.
4. If you want to do this for several windows, go to the windows
properties spreadsheet, change display mode to 'Fins & Overhang', and change
the overhang properties here. You can edit numbers for one window and copy
them for others.
Regards,
Charudatta Joshi (CJ)
MS-Building Design
Graduate Teaching Assistant
Arizona State University
-------------------------------------------
Email: csjoshi at asu.edu
Phone: 480-748-7340
On Tue, Mar 10, 2009 at 4:43 AM, Teck Chew <chew3yuffie3 at yahoo.com> wrote:
>
> Hi all,
>
> Is there a way to model all the window overhangs at 30 degree downward tilt
> instead of 90 degrees (default) in eQUEST?
>
> Any suggestion will be much appreciated.
>
> Thank you
>
> Warmest Regards,
> TC
>
>
>