[Bldg-sim] Building Infiltration

Andy hoover andyhoover at thebestconsultant.com
Tue Mar 10 18:12:50 PDT 2009


In addition to what Craig says below the very idea that it is okay to blow
energy out of the building or suck in unconditioned air at a high, variable,
uncontrolled rates due to high leakage through the envelope in both
directions dependent upon pressure differentials  is certainly not very
'green' or energy saving at the least and we feel contributes to much higher
energy use than necessary and we know it contributes to higher maintenance
costs and lowered useful life of building envelope components.  Because it
is not easy, is not something that HVAC manufacturers/companies/ ASHRAE can
contend with, and requires knowledgeable on site inspection during
construction/remodel/repair it does not get the attention it deserves.  My
belief is that it is a significant contributor to why modeling software does
not match up well with reality.

 

Furthermore, someone please take me to any existing 10 (heck 5) story or
taller  building that does not desperately try to suck in air low and spew
it out high and any low rise with meaningfully controlled building envelope
conditioned air management.  It is almost impossible to find complete vapor
barriers where they need to be at wall/roof interfaces let alone the rest of
it.

 

We have seen these same issues in LEED certified, yes certified, new
buildings as the reward is low for actual building envelope air and moisture
penetration control (versus showing a design and calculation that shows it
is low) and no one is interested in inspecting and making sure the work is
done to meet LEED, heck even base code, requirements because so far there is
zero penalty (LEED, code, GBI, or anyone else).  The energy savings for
existing buildings can be significant and the lowered repair and maintenance
costs for the building envelope are significant if air and moisture
penetration are controlled but the emphasis is certainly not there most of
the time.  

 

My feeling is that we absolutely should reward with LEED points, attaboys,
smiles, pats on the back, tax credits, and everything else we can things
done to existing buildings that increase the useful life of components,
lower environmental impact, lower maintenance requirements and costs, and
decrease energy usage.  I thought that is what the goals were, ACTUAL
lowered environmental impact in all ways and lowered costs.  Building
envelope infiltration gets only lip service and design but there are no
inspection standards and accountability to prove the work is done
appropriately.

 

 

Andy Hoover

Principal

The BEST Consultant, Inc.

Office: 678-200-7648

Fax:678-827-0574

Cell: 678-793-1159

 

www.thebestconsultant.com

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of C. J. Gann
Sent: Tuesday, March 10, 2009 2:01 PM
To: 'Todd Lagus'; 'Karen Walkerman'; 'Mark Prince'
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Building Infiltration

 

Here's my take on it. The baseline building envelope on a renovation is
supposed to be modeled in the pre-renovated condition. This would include
wall and window thermal properties (U, SHGC, etc.) as well as infiltration
estimates. The proposed design would incorporate all changes and
improvements to the envelope and be modeled as such. It should be noted
however that Section 5.4.3 of 90.1-2004 contains mandatory provisions for
air leakage so the proposed design must at least meet the mandatory
requirements.

 

It is unrealistic to assume a positive pressurization strategy eliminates
infiltration. Keep in mind infiltration occurs due to the vapor pressure and
air pressure differences across the envelope. During unoccupied periods fans
usually do not run so a positive pressurization strategy will not work if
fans are off. During the evenings and weekends the vapor pressure will
equalize from inside to outside bringing in any vapor in this air. Blower
door tests are not practical for most commercial buildings due to the large
volume of air movement required to create a pressure differential. Central
AHU supply and exhaust fans could be used with DDC controls to measure air
leakage provided flow measuring instrumentation was installed.

 

Regards,


Craig J. Gann, P.E.

 

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Todd Lagus
Sent: Tuesday, March 10, 2009 9:45 AM
To: Karen Walkerman; Mark Prince
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Building Infiltration

While I agree that there is oversight in not giving credit to reduce
infiltration, I do not feel like LEED credit should be given if there isn't
an established baseline.  Say, for example, the building infiltration was
exceptionally poor.  Improving the building to even average infiltration
performance may have a large effect on the energy model, and LEED points
would be given for a building that may or may not deserve it.  While
improving the infiltration issue saves energy for the owner, there is no
guarantee that the building does not perform poorly.  Maybe there should be
a LEED "most improved" award which uses existing conditions as the baseline.

 

Todd Lagus, EIT

Mechanical Engineer

Sebesta Blomberg 
sebesta.com | P  651.634.7236 | F  651.634.7400

 

This message has been sent via the Internet. Internet communications are not
secure against interception or modification. Sebesta Blomberg therefore can
not guarantee that this message has not been modified in transit. This
message and any files transmitted with it are confidential and intended
solely for the use of the addressee. If you have received this message in
error please notify the sender and destroy your copies of the message and
any attached files.

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Tuesday, March 10, 2009 9:33 AM
To: Mark Prince
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Building Infiltration

 

There aren't any.  There are a few standards that have infiltration
baselines.  I believe the HERS (Home Energy Rating System) uses an
infiltration baseline of about 0.35-0.4 ACH, and there are some other
standards out there.  Of course, some people will argue that the building
should be positively pressurized so that there will be no infiltration.  I
don't know of anyone that has gotten credit for LEED EA C1 for infiltration,
but in my opinion, this is a huge Appendix G oversight.  My suggestion is to
apply for a CIR and suggest an infiltration baseline.  If the building is
100% renovation, the baseline could be established using a blower door test
on the original building, or you could come up with another reasonable,
established baseline.

--
Karen

On Tue, Mar 10, 2009 at 10:16 AM, Mark Prince <mprince at aeieng.com> wrote:

Hello,

I'm involved with a project that is considering pursuing LEED certification.
It is a remodel/renovation of an existing office building.

The existing office building has quite a bit of infiltration.  As part of
the renovation process, the exterior walls are being sprayed with a foam
insulation that will significantly reduce this infiltration.  Someone has
asked the question, if we can take credit for this reduction in
infiltration.  In other words, they want to model the Appendix G baseline
building with the old infiltration rate and model the proposed building with
the new infiltration rate.  This will show a good amount of energy cost
savings.

Is this acceptable?  I'm having a difficult time finding any reference to
infiltration rates within Appendix G.

Thanks,

Mark Prince
Affiliated Engineers
5802 Research Park Blvd.
Madison, WI 53719
(608) 441-6668
mprince at aeieng.com

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

 


  _____  


If this email is spam, report it here:
 
<http://www.onlymyemail.com/view/?action=reportSpam&Id=NzQ3NjI6ODYxOTAxMjgwO
nRsYWd1c0BzZWJlc3RhLmNvbQ%3D%3D> http://www.OnlyMyEmail.com/ReportSpam 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090310/57691a43/attachment.htm>


More information about the Bldg-sim mailing list