[Bldg-sim] Window overhangs at 30 degrees

Charudatta Joshi (CJ) csjoshi at asu.edu
Tue Mar 10 06:34:50 PDT 2009


Teck,


   1. You will need to be in the 'Detailed Data Edit Mode' to be able to
   accomplish this.
   2. Once there, check the properties of a window and get to the
   'Fins-Overhang' tab.
   3. Change the angle (OAng) to 60 degree - that will actually give you the
   30 deg downward tilt you want.
   4. If you want to do this for several windows, go to the windows
   properties spreadsheet, change display mode to 'Fins & Overhang', and change
   the overhang properties here. You can edit numbers for one window and copy
   them for others.


Regards,

Charudatta Joshi (CJ)
MS-Building Design
Graduate Teaching Assistant
Arizona State University
-------------------------------------------
Email: csjoshi at asu.edu
Phone: 480-748-7340

On Tue, Mar 10, 2009 at 4:43 AM, Teck Chew <chew3yuffie3 at yahoo.com> wrote:

>
> Hi all,
>
> Is there a way to model all the window overhangs at 30 degree downward tilt
> instead of 90 degrees (default) in eQUEST?
>
> Any suggestion will be much appreciated.
>
> Thank you
>
> Warmest Regards,
> TC
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090310/34220734/attachment.htm>


More information about the Bldg-sim mailing list