WINDOW 5/WINDOW6 imports Optics database, user portion, not .usr files.  
So when you are done generating laminate, select User Database from the 
toolbar (there is choice of Main db and User db). You should be able to 
see your laminate that you generated (under Laminate category).  Then 
simply close Optics, open W5 or W6 and in Preferences, under Optical 
Data tab, click on radio button "Optics 5 User Database and make sure 
that it is UserGlazing.mdb under LBNL Shared subdir (this is all deafult 
for OPTICS, so if you did not change path in OPTICS this should work, 
otherwise you need to navigate to correct mdb file).  Then close 
preferences, go to Glass library and click on Import, select "IGDB or 
Optics User Database" from the drop down menu under Format and click 
OK.  If everything is right, you will see your laminate that you created 
in OPTICS and will be able to import it.

Charlie Curcija
DesignBuilder Software

-------- Original Message --------
Subject: [Bldg-sim] Optics5
From: Lam, Linda <linda.lam at wspfk.com>
To: bldg-sim at lists.onebuilding.org
Date: 6/30/2009 6:43 PM
> Has anyone successfully created an Optics5 file and imported into 
> Windows5 or 6? I have a pretty complex glazing system that is composed 
> of various coated glazings, and plastic.  I think I've managed to 
> create and save a "Laminate" made of components and adhesive layers 
> but I don't know where to go from here.  It looks like the laminate is 
> saved with a .usr extension.
>  
> When I click "Import" in Windows5, it opens up glazing.mdb but the 
> laminate i created in Optics5 doesn't show up...
>  
> Any help is greatly appreciated!
>  
> Thanks!
> Linda
>  
> Linda Lam, LEED® AP WSP Flack + Kurtz 405 Howard Street, Suite 500 
> San Francisco, CA 94105 Direct: 415.402.5813 Main Tel: 415.398.3833 
> Fax: 415.433.5311 website: http://www.wspfk.com vCard: 
> http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.vcf 
> image:  
>  
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>   

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090630/b0269a74/attachment.htm>


More information about the Bldg-sim mailing list