I'm not sure I follow you. By cycling with occupancy do you mean that the
system must provide ventilation air while occupied? If that's the case
then the fans would never turn off during occupied hours and then would
cycle with the load during unoccupied hours.
Why would you not model a heating system in the proposed building? The
scenario is for a warehouse that has heating but no cooling. I don't see
a requirement anywhere in Appendix G for the baseline and proposed to have
the same fan system, so I believe when it states that the same cooling
system is to be modeled in the baseline and proposed they mean just the
cooling coil and heat rejection device.
Robby Oylear, LEEDR AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www. <http://www.rushingco.com/> rushingco.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
Shariq_Ali at URSCorp.com
Sent: Tuesday, June 23, 2009 12:32 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Bldg-sim Digest, Vol 19, Issue 20
Robby - the fans must cycle with occupancy, and then when the space is not
occupied the must cycle with load. They can not cycle with load only. For
Mike Kennedy's system he would need to model the baseline with VAV heating
and cooling. And also model the same system in the proposed, however you
could set the heating coil capacities to zero, not create a heating plant,
or not assign any systems to the heating plant for the VAV system. (This
is if you are using Trace 700).
Good luck.
-Shariq Ali
This e-mail and any attachments contain URS Corporation confidential
information that may be proprietary or privileged. If you receive this
message in error or are not the intended recipient, you should not retain,
distribute, disclose or use any of this information and you should destroy
the e-mail and any attachments or copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090623/f67bcf50/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 59935 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090623/f67bcf50/attachment.jpeg>
More information about the Bldg-sim
mailing list