Marcus,
 
Even if the same rate structure is used in both buildings, wouldn't the
proposed building be able to take advantage of off-peak rates since its
chillers are running during the night to produce ice, instead of during
the day as in the reference building?
 
Thanks,
Luka

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Marcus
Sheffer
Sent: Tuesday, June 09, 2009 5:39 PM
To: 'Julia Beabout'; BLDG-SIM
Subject: Re: [Bldg-sim] LEED EAcr1 and ice storage?



The metric in LEED (ASHRAE 90.1) is energy cost not energy usage.  I am
certain that ice storage systems have been submitted and approved in
LEED projects.  As currently set up you don't get full credit since both
models must use the same rate structure but you could get some credit
against standard cooling systems if the rate structure favors off-peak
usage.

 

Marcus Sheffer

7group

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Julia
Beabout
Sent: Tuesday, June 09, 2009 5:09 PM
To: BLDG-SIM
Subject: [Bldg-sim] LEED EAcr1 and ice storage?

 

Hi All,

Has anyone successfully submitted an energy model to LEED for NC, EAcr1
compliance that utilized an ice storage system for cooling?

 

I'm just curious if they considered this a valid way to meet EAcr1 since
even though these systems save money (which is the basis for EAcr 1
compliance), they frequently use the same or even more energy than a
standard chiller plant/system design.  In other words, in principle, if
your proposed building uses the same or more energy than your baseline,
but shows a $ savings relative to the baseline, is that still valid.

 

We're considering looking at ice storage for a LEED project I'm working
on.  But, before we run down that route, I'm trying to determine if LEED
considers it an acceptable way to meet EAcr1 and if anyone has been
successfully awarded LEED certification with it.  I tried searching the
CIRs, but the LEED search engine didn't return any matches.  There was a
little traffic on Bldg-sim on it, but that was pretty old (2005).  I
also sent LEED customer service the questions along with a brief
description of ice storage and the not-so-green as well as green aspects
of it.  But, it was obvious by their reply that they had no idea what I
was talking about?!?!?  

 

Any experience you all have regarding ice storage and successful LEED
submittals would be great.

Thanks.

Julia

 