[Bldg-sim] chilled water pump power
Zhuolun Chen
chenzhuolun at hotmail.com
Fri Jan 9 08:34:44 PST 2009
Hi, Itzhak
I want to know that if the 22 w/gpm is the total of primary and secondary pumping, how can I divide this total value into the two system? Is there a factor or something I can use?
ZL Chen
From: Itzhak Maor
Sent: Friday, January 09, 2009 7:55 AM
To: William Bahnfleth ; James V. Dirkes II P.E. ; xiaodongyi at hotmail.com ; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] chilled water pump power
Hello Bill
You are correct. The 22 W/GPM is combined Primary and Secondary pumping. The assumption that used to derive this number is total head of 75'.
Thanks
Itzhak
Itzhak Maor Ph.D., P.E., C.E.M
Manager, Energy Efficiency Services
Global Workplace Solutions
Building Efficiency | Energy Services
Johnson Controls, Inc.
1617 JFK Blvd., Suite 1140 | Philadelphia, PA 19103
Tel.: (215) 241-9111 ext. 14 | Fax: (215) 241-0113
Cell: (215) 767-4582
Itzhak.Maor at jci.com | www.JohnsonControls.com
Please note my new email address, effective November 1st (and useable in the interim).
--------------------------------------------------------------------------------
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of William Bahnfleth
Sent: Thursday, January 08, 2009 7:52 PM
To: James V. Dirkes II P.E.; xiaodongyi at hotmail.com; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] chilled water pump power
I sincerely doubt it.
A fairly typical total pump head for plant and distribution for a primary/secondary systems might be 100 -120 ft. (Note, I am not saying that is GOOD practice, but it is typical. One can generally do better.)
Let's say that the overall efficiency of pump, motor, and drive is ~85%.
If we use the common engineering approximation HP = (Q*H)/(3960*eta_t), and given that 1 HP = 745.7 W, the power associated with 1 gpm and 100 ft wg head is
W = 745.7*(1*100)/(3960*0.85) = 22.15
I cannot think of a reasonable scenario under which 44 W/gpm could be construed to represent minimally acceptable practice.
Bill Bahnfleth
At 07:14 PM 1/8/2009, James V. Dirkes II P.E. wrote:
Good question! My guess is that each pump may be 22W / gpm. Since they are required to use variable speed drives (for >300T), it won't affect energy adversely.
There may be an ASHRAE clarification on this topic; have you checked with them?
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" />
------------------------------------------------------------------------------
From: bldg-sim-bounces at lists.onebuilding.org [ mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of xiao dongyi
Sent: Thursday, January 08, 2009 6:18 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] chilled water pump power
Hi,
I have a question regarding the chilled water pump power calculation in ASHRAE 90.1 Appendix G:
ASHRAE 90.1 Appendix G Paragraph G3.1.3.10 requires that "The baseline building design pump power shall be 22 W/gpm.". If the chilled water pumping system is a primary-secondary system, how does this rule apply? i.e. does the 22 W/gpm apply to the primary pump, secondary pump, or both? Or, do I need to divide it between the primary and secondary pump?
Your suggestions will be greatly appreciated.
Thanks,
Dongyi
------------------------------------------------------------------------------
Windows Live™: Keep your life in sync. See how it works.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
__________
William P. Bahnfleth, PhD, PE, FASHRAE
Professor of Architectural Engineering and Director, Indoor Environment Center
Penn State / 104 Engineering Unit A / University Park, PA 16802 USA
voice: 814.863.2076 / fax: 814.863.4789 / e-mail: wbahnfleth at psu.edu
http://www.engr.psu.edu/ae/faculty/bahnfleth/ , http://www.engr.psu.edu/ae/iec
It is better to know less than to know so much that ain’t so. - Josh Billings
--------------------------------------------------------------------------------
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090109/abb74b2b/attachment-0001.htm>
More information about the Bldg-sim
mailing list