[Bldg-sim] System Fan Power in Appendix G
Kendra Tupper
ktupper at rmi.org
Tue Jan 20 10:42:14 PST 2009
Option 1 the user¹s manuals are a bit more clear, and specify that the its
is the supply cfm that should be used to calculate the fan power. This fan
power includes supply, return and exhaust.
On 1/20/09 11:29 AM, "Zeng, Ming" <mzeng at leoadaly.com> wrote:
> My understanding is option 1. The fan energy in that formula is the sum of all
> the fan horse power. Search the board, I think there is a previous email from
> Michael Rosenberg talking about the fan energy. Hope this helps.
>
>
> Ming Zeng, PE, LEED® Accredited Professional
>
> Mechanical Engineer
>
>
>
>
> 730 Second Avenue South, Suite 1100, Minneapolis, MN 55402-2455
>
> T 612.338.8741 F 612.338.4840 D 612.341.9539
>
> www.leoadaly.com <http://www.leoadaly.com> MZeng at leoadaly.com
>
> Please consider the environment before printing.
>
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mike Kaufman
> Sent: Tuesday, January 20, 2009 12:16 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] System Fan Power in Appendix G
>
> Hi All,
>
> I have a specific question about using Appendix G3.1.2.9 to calculate baseline
> system fan power (I have already searched previous posts and could not find
> the answer I¹m looking for). So, the Appendix G section reads as follows:
> System fan electrical power for supply, return, exhaust, and relief (excluding
> power to fan powered VAV boxes) shall be calculated using the following
> formulas. I understand the formulas, which essentially use a fan CFM to
> determine a brake horsepower BHP, which is then used to calculate the fan
> power (Watts), but my question is this: Supposing you have an HVAC system
> with supply, return, and small exhaust fans (in restrooms, for example) how
> do you calculate the power to each fan?
>
> Option 1: Use your supply fan cfm to calculate a power, say it comes to 10
> kW, and use this as your total ³system² fan power. This 10 kW, being your
> whole system power, is then distributed among all of your system fans however
> you desire (For example, supply fan power = 5 kW, return fan power = 4 kW,
> exhaust fan power = 1 kW, for a total of 10 kW for the fan system)
>
> OR
>
> Option 2: Use each supply, return, and exhaust fan cfm to separately
> calculate an individual kW for each fan (For example, supply fan power = 10 kW
> using the supply cfm, return fan power = 9 kW using the return cfm, exhaust
> fan power = 1 kW using the exhaust cfm, for a total of 20 kW for the whole fan
> system)
>
> Obviously, you will have much more fan energy in a baseline system calculating
> fan power with Option 2. Does anyone have a specific example they can share
> of a fan system calculation that was accepted by USGBC for an EAc1 energy
> model?
>
> Thanks for your help!
> Mike
>
>
> Mike Kaufman, Building Performance Engineer 130 W. 5th Avenue, Denver,
> CO 80204 (NOTE NEW ADDRESS) t 303.278.1532x206 | f 303.278.8533 |
> ambient-e.com <http://www.ambient-e.com/>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090120/34e1624b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4935 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090120/34e1624b/attachment.jpeg>
More information about the Bldg-sim
mailing list