[Bldg-sim] DCV and Enthalpy Economizer
Shaun Martin
smartin at shaunmartinconsulting.com
Mon Jan 19 08:39:15 PST 2009
Hi Janne,
This appears to be a bug in equest - free cooling should override DCV. I
ran into the same problem a few months ago, and found no solution other than
post-processing hourly report data.
Shaun
Shaun Martin LEED AP
Principal
Shaun Martin Consulting
504-318 Homer Street
Vancouver BC V6B 2V2
t: 604-789-1095
e:smartin at shaunmartinconsulting.com
member CAGBC, ASHRAE
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kairento, Janne
Sent: Thursday, January 15, 2009 12:28 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] DCV and Enthalpy Economizer
Hi All,
I'm currently working on a model that has CO2 sensing in a few large high
occupancy spaces. When I select DCV Return Sensor with a minimum OA sizing
method of 'Sum of Zone OA', it drives up the energy consumption of my
electric centrifugal open chillers during the winter months (this is in
climate zone 5A). But without the DCV Return Sensor, there is no space
cooling energy consumption during the winter months. It appears as if the
DCV Return Sensor is overriding the Enthalpy Economizer with a drybulb high
limit of 70F. Does anyone have any insight into what is happening?
Thank You,
Janne
Janne Kairento, E.I.T., LEED AP
Cosentini Associates
A Tetra Tech Company | Complex World, Clear Solutions
One Broadway
Cambridge, MA 02142
Phone: 617.494.9090
Fax: 617.494.9292
Please consider the environment before printing this e-mail
NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any)
are intended solely for the use of the addressees hereof. In addition, this
message and the attachments (if any) may contain information that is
confidential, privileged and exempt from disclosure under applicable law. If
you are not the intended recipient of this message, you are prohibited from
reading, disclosing, reproducing, distributing, disseminating or otherwise
using this transmission. Delivery of this message to any person other than
the intended recipient is not intended to waive any right or privilege. If
you have received this message in error, please promptly notify the sender
by reply E-mail and immediately delete this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090119/b592b1a5/attachment.htm>
More information about the Bldg-sim
mailing list