[Bldg-sim] Appendix G - Exhaust Air Energy Recovery/Number ofBaseline Fan Systems
Ulrik Welle-Strand Horn
ulrik.horn at silpainc.com
Mon Jan 12 22:39:13 PST 2009
Dear Mr. James V. Dirkes II:
Maybe we are using two different simulation programs? I am using Trace 700.
I have confirmed by experiments that the size of the system, or rather the
number of systems, has a significant impact on annual energy consumption.
For certain system types, this should not even be that case, but somehow, in
the calculation procedures of the software, the number of systems somehow
enters the calculations and affects the results. I know it should not be
this way and I have warned the engineers at Trane about the behavior.
Regarding the sizes of coils and fans in air handlers, I was really looking
for a specific value. In a 40 story office building, for example, what are
typical ventilation fan sizes? Does 10,000 cfm sound like a reasonable fan
sizes?
Thank you for helping me out!
Sincerely yours,
*Ulrik Welle-Strand Horn *
Sustainability Engineer
*Silpa Inc.*
*s* i m p l e . *s* c i e n t i f i c . *s* u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com
India: +91.90080.96083
On Mon, Jan 12, 2009 at 9:06 PM, James V. Dirkes II P.E. <jvd2pe at tds.net>wrote:
> p.s.,
>
> You can get a custom air handler and coils with almost any capacity you can
> dream of. In the case of coils, multiple coils can be used in a single air
> handler. It's not so common to use very large air handlers because of space
> restraints and distribution issues, but there are plenty of them in use.
> Once again, the model doesn't care about physical size, only physics :)
>
>
> *The Building Performance Team
> **James V. Dirkes II, P.E., LEED AP
> *1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
>
> ------------------------------
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Ulrik Welle-Strand
> Horn
> *Sent:* Saturday, January 10, 2009 5:15 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Appendix G - Exhaust Air Energy Recovery/Number
> ofBaseline Fan Systems
>
> Dear All,
>
> I am curious how many systems or fan systems most of you usually create
> when you model baseline systems?
>
> I am particularly interested because under point G3.1.2.10 - Exhaust Air
> Energy Recovery, one only has to apply an energy recovery device if a single
> fan system is larger than 5000 cfm. I have not seen anywhere (please direct
> me if there is indeed prescriptions for this in an ASHRAE publication)
> guidelines for how many fan systems one has to model in a baseline building?
> It seems that if I have a building with let's say 15000 cfm supply air, I am
> free to model this building's baseline system with either 2 or 4 fan
> systems? Then, if I model this building with 4 fan systems (each system
> sized equally at 3750 cfm), I would not have to use energy recovery in the
> baseline building, while if I choose to model the baseline with 2 fan
> systems (each sized equally at 7500 cfm), then I must use energy recovery.
>
> I would also appreciate input on a typical size of a fan system. If I have
> a building that has a supply design air flow requirement of 100,000 cfm, how
> many fan systems would typically be modeled? I am not too familiar with HVAC
> design, and I tried looking for clues at manufacturers' websites but only
> Carrier indicated an upper threshold of about 150 tons for their coils. Does
> anyone have an experience with a typical airflow for a very hot climate over
> a 150 ton coil? I am looking at System 8 for my baseline building, and I
> imagine that for a large building (35 stories), several coils will be
> installed. I am using Trace to do the energy model, and for some reason, the
> more systems I model the higher the energy usage, keeping everything else
> constant. Therefore I am interested in modeling several fan systems, if that
> is common design practice.
>
> Lastly, I would like to confirm that the design of the baseline system
> beyond what is stipulated in Appendix G should comply with common practice?
> In particular, numbers and sizes of systems does not seem to be much
> discussed in Appendix G. Please let me know if you share my approach in
> applying common design practices to size and locate equipment beyond
> Appendix G prescriptions.
>
> I appreciate any feedback you might have on these issues.
>
> Faithfully yours,
>
>
> *Ulrik Welle-Strand Horn *
> Sustainability Engineer
>
> *Silpa Inc.*
> *s* i m p l e . *s* c i e n t i f i c . *s* u s t a i n a b l e
> AMERICAS | MIDDLE EAST | ASIA
> www.silpainc.com
>
> India: +91.90080.96083
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090113/7cafc954/attachment.htm>
More information about the Bldg-sim
mailing list