[Bldg-sim] Modeling Baseline Exterior wall for Renovation

Alex Chapin alexc at 2rw.com
Mon Jan 12 12:32:18 PST 2009


The way it works is as follows:

-Step 1, Compare proposed model to baseline model with existing wall and use this to achieve points
(p. 181 of LEED NC 2.2 EA Credit 1 Calculations Section)

-Step 2, Compare proposed model to baseline model with ASHRAE 90.1 walls as a check to make sure proposed is at least this efficient
(At the moment I can't remember where I read this, maybe a CIR? Can anyone confirm this?)

Alex Chapin, E.I.T., LEED AP
Energy Engineer
2rw Consultants
T: 434-296-2116 ext. 101
F: 434-977-1862


Date: Mon, 12 Jan 2009 10:49:36 -0500

From: "Gaiko Allison" <Allison_Gaiko at aha-engineers.com>

Subject: [Bldg-sim] Modeling Baseline Exterior wall for Renovation

To: <bldg-sim at lists.onebuilding.org>

Message-ID:

      <3C61A3A4F1F6F045858CAB5C84CDDCF7040B8FDE at fs7.aha-engineers.com>

Content-Type: text/plain; charset="us-ascii"



I am working on a renovated building and am wondering whether the

baseline exterior wall should be the current existing wall or the

baseline wall system as described by ASHRAE 90.1.  If it matters, we are

going for LEED NC points because of the extent of the renovation, not

LEED EB.







Does anyone have any experience with this?






Allison Gaiko, PE, LEED AP
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090112/ba9ac50c/attachment.htm>


More information about the Bldg-sim mailing list